PLC 5-15 powers up in remote program mode

don1969

Member
Join Date
Jan 2005
Posts
9
I have a 1785-LT B PLC 5/15 processor that on power up starts up in remote program mode instead of remote run mode. The key switch is in remote. I have never seen this before, all our processors are set in remote mode and always start up in remote run mode. Any ideas? Thanks, Don.
 
get online and change the processor status to run,there is a drop down on the top left that at the moment will be in "remote".the key switch can be in either "remote" or "run".
 
If you have an EPROM stuck in the bottom of the processor it may be loading off the EPROM on start. In that case I think it will start in program mode.

Keith
 
Long time since I was in affairs with AB 5/15, but I recall that this is a DIP switch setting in the chassiss it self, if I still remember it is no 8.


Cheers
Hagos
 

Similar Topics

Hello all. I recently had to re install my AutoCAD Electrical 2024. I am trying to find the Rockwell catalog to install in it but cant find...
Replies
0
Views
60
Hello, I have an issue where I want to simulate an Siemens HMI panel, through NAT connection to a PLC. I have the possibility through extended...
Replies
1
Views
41
I had a call yesterday that a light had come on, on the panel saying 'battery low' and what it meant and which battery? This was from a program I...
Replies
4
Views
137
Hello, im quite new and still learning. I would like to ask is it possible for FATEK PLC to read data value more than 16k? I'm trying to move my...
Replies
0
Views
69
Hi all, looking to model old RR relays in PLC. Does anyone have any SPECIFIC examples on how to model a relay such as a polar relay, slow pickup...
Replies
0
Views
96
Back
Top Bottom