DumbHammerMechanic
Hello all. Been reading for a long time, 1st real post. AB was unable to help me beyond "Yeah, that's old, we think you should upgrade..." which would be nice, but I'm just a maintenance man, so my job is to fix it.
We have 15 AB PF40p conveyor drives on a ControlNet chain. This was installed about 8 years ago, and has given us problems with several drives since install. This was converted from a contactor on/off set up, to drives. The main issue is comm loss. Either one or more drives will stay running after being commanded to stop, or one or more drives will stay off when commanded to start. The easy button is logging into the PLC5000, and resetting the CNet card, which gets us going 99 of 100 times. Occasionally, we will have to power off the drive entirely, and reset the comms to get the drive talking again.
I wont go into complete detail the things we've done to remedy this, as this post would be PAGES long, but the basics are as follows:
OHM tested all T-post junctions. Replaced the ones on the drives that most frequently give us issues. None tested out of range.
OHM tested the trunk line. no out of spec measurements.
REPLACED all of the trunk line. New high end connectors, top quality cable, a $400 crimper set, the works, all on the recommendation of AB, all their parts. ***This did help reduce comm loss and noise about 70%, but its still not as reliable as our newer ethernet drives.***
Replaced several drive mounted CNet COMM cards, on drives whos failure rate is higher.
Noise insulated the trunk line, routing it away from lighting, load power cables, etc.
There is a lot more we have done, so if you think of something ask away, we will either try it or confirm it.
Is anyone running an ControlNet system successfully with near zero comm errors and noise? This whole thing is confined to the MCC, so total cable length is under 50FT. I've seen CNet used in airports with thousands of feet of cable, and while it had its issues too, comm drop and control loss wasn't one of them.
Thoughts?
-J0N
Thoughts?