Hello

S7-200 CPU 224 CN is installed and SM31.7 is used for data write to EEPROM

Now I have uploaded the program from CPU 224CN and downloaded it to CPU 224 standard

problem is that when I set SM31.7 then it does not go back to 0 state and remains ON

what may be the reason?

waiting
 
Hello
According to the manual, SM31.7 goes to zero automatically after writing values
In Old cpu 224 cn , this function is working properly. When I set it, it becomes 0 automatically
But in cpu 224, it is not working. When i set it to 1, it remains 1
Please suggest solution
Thanks
 
So it looks ok - I would suggest you go online and check each network where SM31.7 occurs to see if eg. M18.5 / M18.6 / V2000.4 etc are being "re-triggered" in the program?
 
M18.5 M18.6 etc are triggered from hmi
So there is no chance of being triggered inside plc
Moreover, same plc program works fine with old cpu 224 cn
 
Have you been online and checked?
What is the status of SM0.0
What is the value in SMW22
Failing this then the save function has not "finished" - (maybe a corrupt EEProm ? DB)?
 
I will check the status of SM0.0 and value of SMW22
so if it seems that the issue is due to some corrupt EEPROM then what is the solution?
 

Similar Topics

Hi all, Currently having trouble getting a speed reference to write over modbus to an Omron M1... I can successfully write a run command and...
Replies
2
Views
36
HI i would like to know how to get a variable that will store the amount of times a program has been executed. The issue is I have 3 DBs for 1 FB...
Replies
2
Views
63
Hi folk, I would like to know what kind of Parameters should I setup for controlling with Profibus. My old Lenze 8200 motec 0.25kW have a busted...
Replies
0
Views
63
Hi, I have attached herewith one image which our programmer has been used in S7 1500 PLC. Now we need to use the same instructions in S7 1200 PLC...
Replies
4
Views
114
commentaire communiqué siemens s7-1200 avec vfd delta ? (cablage et sur tia portal )
Replies
0
Views
89
Back
Top Bottom