I/O list in omron plc

rezarahnama

Member
Join Date
Dec 2022
Location
Tehran
Posts
3
Hi everybody
i always work with TIAPORTAL and i can read I/O addresses from TAG section, but in the CX-Programmer for omron plc i dont know how to access to the tag list or I/O list of the project. i want to know the addresses of all input and output in the PLC to check the project. Because the project is wroten by somone else, there is no any information about the input/output.
best regards
 
You have not said which processor or I/O cards etc.
All inputs & outputs are in the CIO area CI0.0 - 15 CIO99.0 -15
are the inputs CIO 100.0 onwards are the outputs.
 
You have not said which processor or I/O cards etc.
All inputs & outputs are in the CIO area CI0.0 - 15 CIO99.0 -15
are the inputs CIO 100.0 onwards are the outputs.
CPU model is the key here
The above is true for all CP1L/H series brick versions
Rack based can be anything in the CIO area
Older versions such as CQM & CPM series, the outputs started from CIO10.00
 
The symbols may have not been saved by the original programmer - there is an option to save or not.
 

Similar Topics

Hi there. I'm pretty new to the world of automation. Our first project our team will be doing is a recommissioning job using OMRON CJ2H PLCs. we...
Replies
14
Views
3,263
I am developing a library in twincat and one of the function uses IID_ITcVnAccess_TcVnPoint2_DINT and the definition of this type is defined in...
Replies
0
Views
70
We are trying to poll data coming from a PLC for remote monitoring we have the IP address of the PLC and the default port number and the path is...
Replies
25
Views
568
Hello, Haven't been on in a while. I need to generate a bit level pdf of the I/O for RSLogix 500. I can generate a report but it just shows the...
Replies
1
Views
157
Hi all, Anyone got Preventive Maintenance Checklist for Rockwell PLCs? I found this article, but it does not clearly talk about PLCs, though it...
Replies
6
Views
437
Back
Top Bottom