MSG timeout - wireshark shows constant retransmissions

ASF said:
...Using the web interface for the switch, I don't know of any way to set a port up to mirror two ports at once. I don't think it's possible...

robertkjonesjr said:
From the Stratix user manual:

Quote:
You can configure port mirroring on only one port via Device Manager.
However, you can configure multiple ports via the CLI.

970047 - Multiple Port Mirroring Sessions on a Stratix switch
Access Level: TechConnect

(Workaround 2)

Yes, for the Stratix switches, which are essentially Cisco IOS, this is quite possible via the CLI.

G.
 
I don't know the Stratix series, but I do know the usual Cisco IOS platforms, as well as others and this is actually a common issue - having two source ports set to a single destination like this. From the Stratix user manual:
You can configure port mirroring on only one port via Device Manager.
However, you can configure multiple ports via the CLI.
Quite correct, and George's technote backs this up. I was doing this via the web interface though, so it *shouldn't* have been possible? Based on what I've seen so far, and the face that it is possible to mirror from two ports at once, I'm inclined to think that that's exactly what happened, and that there is a bug involved that allowed me to do it from the web interface despite it "not being possible". Quite possibly related, as I mentioned previously, to me not unplugging from the mirroring port between settings.


For general capture use, I started buying these for my team:

https://www.tp-link.com/us/products/details/cat-5711_TL-SG105E.html

You can set a mirror port so acts just like a tap; and on Amazon, it's less than $30US. But it needs a power supply / wall wart. Some of those other ones are USB powered, so can run off a laptop which can surely be convenient sometimes.

For serious use, if I can't get a span port out of the infrastructure, I had to stop using the FTE device. I found this to be far superior and very easy to use:

https://www.profitap.com/profishark-1g/

But it is in the professional category - it's like $3000 or so.


Whoa, that does look good but I'm sure as hell not selling that one to my boss! :oops:


This one, maybe. Based on your experience, would you say it should be a good bet?
 

Similar Topics

I've got a Controllogix system that is doing a MSG Read from an SLC500 PLC and over the past week we have had multiple issues with the MSG timing...
Replies
11
Views
5,662
Hey guys, I'm seeing some odd behavior with some MSG instructions I have set up. Specifically, when I enable the MSG instruction I nearly...
Replies
5
Views
5,989
I have an 1769-L16ER that I use to test code and I just found that I can't create MSG tags at the local program scope - they have to be done at...
Replies
4
Views
188
I have a client who periodically experiences network communication issues. Sometimes when I VPN into the site, their SCADA systems will flash comm...
Replies
2
Views
158
I'm trying to read/write to an SLC5 with a ControlLogix L71 V35 plc that fails. The exact same code works on an L82S with V32. Is there a known...
Replies
10
Views
285
Back
Top Bottom