Versamax micro Plc Ge fanuc

Dinesh_S

Member
Join Date
Feb 2020
Location
Karnataka
Posts
3
Every time i turn off and turn on the PLC, PLC is not going to RUN mode
In the fault table it shows error " system Configuration mismatch"
And the other fault " battery signal failed"
I did not install/Put any battery
I think it is because of that
Please help me if you think there is any other issue
I have the image file attached, so please check and help

IMG_20200211_175117.jpg
 
Last edited:
Notice that the timestamp for those faults is 22 years ago and the PLC's internal clock is accurate. Just clear the fault table and you should be able to cycle power without issue.
Presumably, every time you've cycled power over the last 22 years you've restarted via the Run/Stop switch on the base unit.
 
System configuration mismatch means there is a difference between the actual hardware in place and the hardware specified in the PLC's hardware configuration. The hardware is the base unit and any expansion modules. Find that difference, make the necessary corrections to the hardware configuration file and send the corrected file to the PLC. If that does not eliminate the system configuration mismatch fault your processor may need to be replaced.
Has this PLC been running for the past 22 years or did you recently purchase it?
 

Similar Topics

Hi, I am trying to set the IP address on the IC200UEM001 Ethernet Option Module. I am following the procedure in the manual for setting a...
Replies
1
Views
425
I'm trying to utilize a PLC that my employer already had on hand for a project. For the life of me, I can't figure out how to get my computer and...
Replies
14
Views
5,089
Hi everybody, I am trying to set PCL time and date from iFix VBA code and I don't even know where to start. Does anybody know the command or...
Replies
3
Views
2,639
Hi, I need to communicate a WinCC Flexible Runtime with a Versamax Micro 64 PLC + ethernet module. This module support protocols SRTP and Modbus...
Replies
1
Views
4,059
I'm having problems connecting with a GE VersaMax Micro PLC. I'm using VersaPro software, com port, to SNP (15-pin) connector on PLC. Connecting...
Replies
8
Views
5,780
Back
Top Bottom