allen bradley coms port

jimmydbkr

Member
Join Date
Feb 2017
Location
texas
Posts
1
I have a L32e Allen Bradly compact logic that keeps losing coms with panel view , I can reset the processor by removing the power, but its not completely fixing the problem .
any ideas????
 
Are you using the serial port to communicate or the Ethernet port?

A long time ago we used L31's and PanelView Plus over serial, the early v17 firmware would behave like this. After a day or so, the comms would drop and only a reboot would cure it. Maybe the L32E's would suffer from the same firmware bug. That's probably a long shot. If you happen to be using v17, I'd make sure that it is 17.7.

If it's over Ethernet, the first place I'd go to is the web page of the L32E. There are some really helpful statistics that you can look at to help diagnose issues. I haven't looked at a L32E's web page in quite a while but something like the diagnostic overview, look for missed and rejected packets, this should be zero. Ethernet Statistics will have a bunch more statistics like FSC, alignment errors, collisions and such, again a normal system they will be zero. The other thing that you have to watch out for over Ethernet is the number of connections. If the L32E is exceeding the number of connections, that could cause your L32E to stop communicating to your PanelView.
 

Similar Topics

Hi Having issues with a older PanelView touch not working. Screen is connected to a Desktop computer. screen used as a display with touch...
Replies
1
Views
74
Hi good day Everyone, I have a cimplicity v10 project with 7 to 8k tags communicating with AB PLC through OPC and Rslinx classic. I have this...
Replies
1
Views
80
Hi everyone, I am currently working on a AB 193-EDN and i am trying to figure out this "Average %FLA", it keeps showing 70-75 but my clamp meter...
Replies
1
Views
83
I am using Allen Bradley PLC 1756-L81E and EIP module 1756-EN2TR for Ethernet/IP communication. My communication works fine but in Get-Attribute...
Replies
2
Views
164
I have a network with 4 PLCs PLC1 is controllogix and PLCs 2-4 are compactlogix and they all need to communicate. The current way I have this...
Replies
8
Views
223
Back
Top Bottom