Clear Scada and M340 communication

Mishtavince

Member
Join Date
Jan 2014
Location
Gulf
Posts
19
Hello.

I need some help.
I'm trying to establish communication between an M340 and Clear SCADA.

I'm trying to establish connection in clear scada via tcp/ip in the DNP3 direct chanel option, but after i enter the ip address, it also wants me to enter the Port no - which i do not know.

the port no is supposed to be the listening port of M340 ( i guess)

If someone has had successful attempts in the past. Kindly share please.
 
To my knowledge, the M340 requires a separate RTU comms module (BMXNOR0200H) to be able to communicate DNP3. The processor itself does not have native DNP3 support.

Assuming you're already aware of this and have procured an RTU module, then the RTU module configuration in the Unity software should allow you to set local port numbers for TCP or UDP comms (depending on which one you're using to transport the DNP3 packets). Just make sure the two settings on the PLC and ClearSCADA align with each other.
 

Similar Topics

Hi Frnds. I have a Technolog make Cello Data Loggers which has got its own Interfacing software named PMAC based on their propriety protocols...
Replies
0
Views
1,567
Hi, Experts: We have 20 + years old GE PLC series 90-30 stop running (the run led not on and battery led not on) and HMI showing that "PLC has...
Replies
7
Views
181
Hi everyone, recently i worked with a cmore panel and have the question that how can clear alarm list whit remote form,right now only can with...
Replies
0
Views
101
Hi guys, I have a data table as REAL type VALUES_TABLE[32,100]. I want to clear this table. For that i created a REAL type CLEAR_DATA tag with...
Replies
8
Views
550
Hi, I have bought a used 1756-L73S and SP, it is running firmware 30.013 and safety locked, im running Logix Designer 30.01.00. The controller...
Replies
10
Views
1,644
Back
Top Bottom