Problem with unexpected movement Kinetix 7000 drive

Mike R

Member
Join Date
Sep 2008
Location
Kent
Posts
13
We have a tissue Embosser which uses AB Kinetix 7000 drives and HPK servo motors. This particular fault concerns a 2099-BM07-S drive controlling a HPK-B1307C-SA42AA motor.

We are having a problem when starting the machine whereby one of the axis moves (apparently) as soon as the drive is enabled.

It seems as if the drive is given the MSO command and then, the motor starts to move instantly, but it is not being given a command to move at this point as far as I'm aware, so the position error increases until it breaches the position error limit and the drive faults on E19 Position Error. This all happens almost instantaneously.

Fortunately, the machine does not have to have the roll drive, it runs against roll and so we have disabled the drive for the affected roll. Ideally it would run under its own power to speed match the other roll which improves the roll cover life.

We have the problem with this axis regardless of whether the drive belt to the roll is connected or not, so it is not the load turning the motor, it is definitely a motor/drive issue

This problem occurs the instant the drive is enabled, it seems to be at the point the Bus lamp goes from flashing green to solid green (which as I said above, I believe is when the MSO command is given).

I set up a trend to monitor command position, actual position, command velocity, actual velocity & position error. You can see the motor turn as the position and velocity feedback changes, but there is no commanded position or velocity and you can see the position error increase.

It just seems like the drive is giving the motor a 'kick' when its enabled.

We had RA in and they just wanted to tune the drive, but it could not complete the Autotune. It also could only complete 2 or the 3 hookup tests (marker pulse and feedback tests, the command and feedback test failed, although it didn't tell us what it failed on). Their engineer left suggesting that we change the motor, but the motor is new (we changed it when we first started having the problem) and it has never run in anger. We have also changed the drive and finally the encoder cable but we still have the same issue. Only thing not changed is the motor power cable.

Any thoughts? I can not work out if its some kind of problem on the power supply or a motion control issue. None of the other motors have the same issue, so assume its motion control problem on this axis, but the machine never used to have this issue either, so something is different.

Any thoughts or suggestions would be greatly appreciated. May take a while to get back as sorting this out is not a priority job at the moment.

Many thanks,

Michael.
 

Similar Topics

We have a tissue Embosser which uses AB Kinetix 7000 drives and HPK servo motors. This particular fault concerns a 2099-BM07-S drive controlling a...
Replies
3
Views
2,535
I have a simple initialization loop FOR BS_i:=0 TO (BS_CONC_LEVEL_CONTROL - 1) DO BSHistorySt_Return_LR[BS_i] := DONT_CARE; END_FOR...
Replies
11
Views
2,402
On all pages of my project i have a lot of information, texts and details that should not not be shown. I can remove them for each part apart from...
Replies
0
Views
28
Hi, I have had problem with upgrading some projects from v16 to v18. I tried it on 3 diffrent computers. I want to post this so that anyone that...
Replies
3
Views
148
Hi, I am having a challenge installing a new drive ACS355-03E-44A0-4 as it keeps on displaying Fault code F00018 even when the load is not...
Replies
3
Views
134
Back
Top Bottom