Colt Hero
Member
ControlLogix 5575 (L75): Sudden/Repeating "Unconnected Message Timeout" (0204)
This ControlLogix PLC (L75/5575) has been in operation for at least 6 years now, is non-redundant, and is directly Ethernet-wired to two "remote" racks that only about 40' of cable away. A couple of weeks ago it started scrolling the "I/O Fault ... Unconnected Message Timeout 0204". The PLC chassis looked fine otherwise, I could remote-connect to it, and the PLC was not Faulted, but in the software - the I/O on one of the remote racks was showing the yellow triangles/"!" on all the I/O. At the cabinet, all the modules had red lights, so I pulled the network plug out of the remote rack, plugged it back in, and everything started working again. About a week or so later, same thing happened, except this time it was the other remote rack directly above (in the same cabinet). Again, I pulled the network cable, which cleared that rack, but then the other rack got hung up ... so I pulled that cable, and everything started working again. I guess these two are daisey-chained?
This has happened now at least two more times. I've seen similar complaints online about this kind of thing. Should I try re-seating the Ethernet Card on the main PLC chassis (since that's the common denominator here), or the card on the remote chassis, or both? And then what ... replace the Ethernet card(s) if the problem returns? How can you tell for sure which end has the problem?
The Ethernet Card on the main PLC chassis is a 1756-EN2TR 10/100 Mbps Ethernet Bridge, 2-port, twisted pair media, rev 10.007.
The PLC itself is a 1756-L75 ControlLogix 5575, Rev 20.54 in a 17-slot chassis.
This ControlLogix PLC (L75/5575) has been in operation for at least 6 years now, is non-redundant, and is directly Ethernet-wired to two "remote" racks that only about 40' of cable away. A couple of weeks ago it started scrolling the "I/O Fault ... Unconnected Message Timeout 0204". The PLC chassis looked fine otherwise, I could remote-connect to it, and the PLC was not Faulted, but in the software - the I/O on one of the remote racks was showing the yellow triangles/"!" on all the I/O. At the cabinet, all the modules had red lights, so I pulled the network plug out of the remote rack, plugged it back in, and everything started working again. About a week or so later, same thing happened, except this time it was the other remote rack directly above (in the same cabinet). Again, I pulled the network cable, which cleared that rack, but then the other rack got hung up ... so I pulled that cable, and everything started working again. I guess these two are daisey-chained?
This has happened now at least two more times. I've seen similar complaints online about this kind of thing. Should I try re-seating the Ethernet Card on the main PLC chassis (since that's the common denominator here), or the card on the remote chassis, or both? And then what ... replace the Ethernet card(s) if the problem returns? How can you tell for sure which end has the problem?
The Ethernet Card on the main PLC chassis is a 1756-EN2TR 10/100 Mbps Ethernet Bridge, 2-port, twisted pair media, rev 10.007.
The PLC itself is a 1756-L75 ControlLogix 5575, Rev 20.54 in a 17-slot chassis.