Honeywell Control Edge900 & HCi Designer Studio

MAKSM

Member
Join Date
Jul 2016
Location
Mumbai
Posts
35
Hello Expert,

I'm now with Honeywell Products.
Can some one advise which connection setting to be used during HMI development using HCi Designer Studio to communicate between Honeywell CPM, ControlEdge 900 (900CP1-0200) & HMI (HCiRW10-TE-FD-NC).
Does HC-900 series same as Control Edge 900 PLC

Thanks

WhatsApp Image 2022-05-11 at 5.23.58 PM.jpeg
 
>Does HC-900 series same as Control Edge 900 PLC?

The I/O modules and rack power supplies are interchangeable.

But the development software for the HC-900 CPU controllers is not the same software that the ControlEdge PLC uses. The HC-900 and the ControlEdge PLC have radically different functionality with radically different software.

The HC-900 HMI, p/n 900CR1x-00 needs to be programmed with ControlEdge HC900 Designer Software, p/n HC-DSGRSW. But you don't reference that HMI.

I don't know what CPM is or the other HMI part number, so they're probably part numbers associated with ControlEdge PLC, which someone else will have to comment on.
 
>Does HC-900 series same as Control Edge 900 PLC?

The I/O modules and rack power supplies are interchangeable.

But the development software for the HC-900 CPU controllers is not the same software that the ControlEdge PLC uses. The HC-900 and the ControlEdge PLC have radically different functionality with radically different software.

The HC-900 HMI, p/n 900CR1x-00 needs to be programmed with ControlEdge HC900 Designer Software, p/n HC-DSGRSW. But you don't reference that HMI.

I don't know what CPM is or the other HMI part number, so they're probably part numbers associated with ControlEdge PLC, which someone else will have to comment on.

The 900CP1-0200 is the ControlEdge PLC processor. While I know what the HCi is, I haven't used it.

Based on the way you set it up, the ControlEdge PLC supports Ethernet/IP, Modbus TCP, OPCUA, and (I think DNP3). There may be others. My recommendation to the OP is that He/She use configure the PLC to use Modbus TCP and use that driver in the HCi.
 

Similar Topics

Hello, friends. I've programmed a ControlEdge 900 PLC (900CP1-0200) and I now have to make an HMI application for a 900 Control Station...
Replies
2
Views
2,036
I am trying to use complex code to make a button blink. I need to OR two digital variables. I can’t find information anywhere on the syntax or any...
Replies
7
Views
2,054
Hello, Without using the Honeywell 900 Control Station starter file, how can you create a button to export all your log files onto a USB stick...
Replies
3
Views
1,721
I am new to HCD (ver 4.403), but I have a problem programming the controller time on my HC900 C50 controller (4.4 FIRMWARE). The controllers time...
Replies
5
Views
3,755
Hello, Does anybody know where the symbols library "resides" on the Honeywell HC900 Control Station Designer Software package? I am trying to...
Replies
1
Views
4,775
Back
Top Bottom