We have 2 Siemens IL-70 PC touchpanels
connected to 2 S7-315-2DP PLCs on seperate
machinery. The machines however are in a production cell. The connection is made through the X2-DP port via profibus.
Also we have a 3rd S7-315 in the same cell
on another peice of machinery. We have
Siemens simatic S7 programming software
installed on both IL-70's for editing or
troubleshooting. If possible how could a change made on one IL-70 PC be automatically updated on the other IL-70 PC? Right now if you make a programming change on one unit the other has a different program.
 
Here is a "relatively" simple way to do it:

Setup both PCs so that they are on the same network and so that they share a backup folder on one of the PCs (or better yet: A server drive).

Before editing the programs, allways use the "retrieve" function to get the latest version of the program.

When using the "archive" function, point to the shared folder for storing the .zip file. Use a version number in the filename and increment it everytime edits have been made.

I dont think it can be done 100% automatically.
Under Options ... Customize ... Archiving , the path for archiving and retrieving can be set.
 

Similar Topics

Trying to integrate a new S7-1500 to an existing S7-300 PLC. Using the S7-1500 as an I/O Device. Trying to send some simple boolean tags between...
Replies
2
Views
1,059
Hi, I'm investigating different network protocols for PLC to PLC comms, and PLC to SCADA. OPC UA seems to be a very useful protocol that I'm...
Replies
4
Views
2,075
Hello, this is a brand new task for me. I recently bought a particulate sensor and it communicates with UART protocol or I2C protocol. It came...
Replies
12
Views
2,809
I have a piece of equipment with control split between two PLCs. A quantum 434, and a Siemens S7-300, communicating via profibus. I have a prosoft...
Replies
14
Views
5,220
Hi All, I have a Simens CU320 drive controller that I wish to connect to via the X127 ethernet port. The unit communicates with the CPU vua...
Replies
11
Views
4,074
Back
Top Bottom