Studio 5000 Message Communication Path

Hi,

I am trying to configure a CIP data table read MSG instruction to read a tag on a L85E controller and write to a L82E controller. The L85 routing is 10.10.114.23,1,0 and the L82E is 10.10.114.111,1,0. I am struggling with the path. My understanding from the programming manual is that my path in the Communication tab would be 1,0,10.10.114.23,1,0. However when I try to enter this I get an error "Use of period of alphabetics is restricted to IP addresses, which cannot appear as the first field of a path. My IP address isn't the first field in my path, so I am confused. Any help would be greatly appreciated. Thanks!
  Reply With Quote
Old May 24th, 2018, 03:11 PM   #2
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 14,174
I think the CIP Path for a 1756-L8 controller is simply "2, IP"

The 2 is for the Ethernet port on the front of the controller when used in Ring mode. If you split and use two IP interfaces, they are Ports 2 and 3.

The "1,0" is not necessary at the end of the CIP Path because the message goes directly to the L8, and does not need to go through a backplane port (1) and 1756 Slot number (0) to get to the CPU.
  Reply With Quote
Old May 24th, 2018, 04:31 PM   #3
Ravioli
Member
United States

Ravioli is offline
 
Join Date: Dec 2015
Location: United States
Posts: 50
I usually need to stop and think, and stop again, and quadruple-check my work every time I manually configure a CIP path.

What I usually do to make it easy is add the path to the other controller in the IO configuration. You have the bonus of knowing the path is right if there's no errors in your IO config. Then enter the named controller in your message instruction. If you now delete the path from the IO configuration, the message instruction will reveal the CIP path.
  Reply With Quote
Old May 24th, 2018, 07:46 PM   #4
Pete_S
Member
United States

Pete_S is offline
 
Join Date: Mar 2015
Location: Portland Maine
Posts: 69
Quote:
Originally Posted by Ken Roach View Post
I think the CIP Path for a 1756-L8 controller is simply "2, IP"

The 2 is for the Ethernet port on the front of the controller when used in Ring mode. If you split and use two IP interfaces, they are Ports 2 and 3.

The "1,0" is not necessary at the end of the CIP Path because the message goes directly to the L8, and does not need to go through a backplane port (1) and 1756 Slot number (0) to get to the CPU.
Thank you Ken, my issue was using 0 instead of 2 caused the syntax to fail as cant get to an IP address directly from the CPU. I am used to using ,1,0 with our Controllogix Ethernet driver to hit the CPU, and forget its different going controller to controller.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Studio 5000 Download to PLC Failure BlueAltezza LIVE PLC Questions And Answers 1 September 24th, 2018 08:48 PM
Studio 5000 revision issue Scotty13 LIVE PLC Questions And Answers 9 March 7th, 2018 06:32 PM
FOR instruction help in Studio 5000 DaveLM LIVE PLC Questions And Answers 7 May 27th, 2017 09:27 AM
Message Instruction Path assignment - looking for ideas Mark Whitt LIVE PLC Questions And Answers 0 May 1st, 2015 11:11 AM
New guy here, question about 1756-L72 and studio 5000 Jasondelane LIVE PLC Questions And Answers 8 March 12th, 2015 04:10 PM


All times are GMT -5. The time now is 01:11 PM.


.