I get a little confuse with MOVD (MOVE Digit) instruction of omron PLC.

According to an explanation I googled, a MOVD instruction has 3 elements: Source (S), Control word (C), Destination (D). The Source (S) is the value to be copied, control word (C) is the manipulator of the "movement", destination (D) is the destination of the copied value starting from the digit specified in C and filling in to the left.

Example:

MOVD DM0 #0132 DM10, DM0 = 5678 (D3=5, D2=6, D1=7, D0=8)

S = DM0
D = DM10
C = 0132 (D3=0, D2=1, D1=3, D0=2)
D0 = 2 (Specifies the 1st digit copied from source, the value must be
from 0 - 3)

Hence, the D2 of DM0, which 6, will be the first to be transferred
to the location specified by D2 of C.
D1 = 3 (Indicates the number of digits to be copied, 0=1 digit, 1=2
digits, 2=3 digits, 3=4 digits)

Since D1 of C = 3, hence we will move all 4 digits of Source to
Destination.
D2 = 1 (Indicates the starting digit that the data will be moved into
the Destination)

The D2 of DM0, which is 6, will be moved to D1 of the
Destination. The rest of the digit will be copied in the same pattern and
wrapping back around to D0.
D3 = 0 (The MSB must always be zero)

Hence result of the "movement" will be:

MOVD DM0 #0132 DM10 (DM0 = 5678, DM10 = 8567)

Continue to next post.........
 
If I have:

MOVD DM0 #0000 101, DM0 = 3 (D3=0, D2=0, D1=0, D0=3)

Hence,

101 = 3
102 = 0
103 = 0
104 = 0

However, 101 is a bit. So how it is going to function having a value of 3?
 
I see.

Hence,

D0 = 101.00-101.03
D1 = 101.04-101.07
D2 = 101.08-101.11
D3 = 101.12-101.15

Meaning if DM0 = 3 with C = 0000, then

101.00 - 1
101.01 - 0
101.02 - 1
101.03 - 0
 

Similar Topics

Hi There, I have couple of Omron PLCs connected on my kepserverex and my intouch reads data from kepserverex. I have been observing that roughly...
Replies
1
Views
47
Hi dear . I have a system with cj1m cpu11 etn. previously NT 5z HMI was connected with plc. recently my old HMI got damaged. I want to replace it...
Replies
5
Views
80
Omron AD081-V1 Analog Input Card Offset & Gain Adjustment Entering Adjustment Mode 1. Set the input card in adjustment mode (Turn ON Dip SW No-1)...
Replies
0
Views
42
I am working on a project using a NB screen and NX1P2 PLC. I am having a really hard time getting a real number to properly translate through to...
Replies
3
Views
114
Hi, I am facing an error inside Omron Network Configurator. I have 2 PLC communicate each other using ethernet cable, send signal using Network...
Replies
2
Views
97
Back
Top Bottom