travispedley
Member
Logix V30, using PIDE
I have a process with a vfd controlling pressure and a flow control valve that controls flow rate. The vfd pumps water from a tank, through some filters and instruments then back into a downstream process.
VFD loop is closed with a pressure sensor.
FCV loop is closed with a flow meter.
They fight each other.
When my process wants more pressure, the VFD pump speeds up. This causes an increased flow to my FCV which chokes the pipe and causes a pressure spike which is driving the VFD loop nuts. The same is true when my process tries to adjust the flow rate. I have gotten them both to tune fairly well, so long as the other loop is in manual. In the end, i need to control both the pressure and the flowrate of the water in the system.
Any ideas or hints for things to try?
I have a process with a vfd controlling pressure and a flow control valve that controls flow rate. The vfd pumps water from a tank, through some filters and instruments then back into a downstream process.
VFD loop is closed with a pressure sensor.
FCV loop is closed with a flow meter.
They fight each other.
When my process wants more pressure, the VFD pump speeds up. This causes an increased flow to my FCV which chokes the pipe and causes a pressure spike which is driving the VFD loop nuts. The same is true when my process tries to adjust the flow rate. I have gotten them both to tune fairly well, so long as the other loop is in manual. In the end, i need to control both the pressure and the flowrate of the water in the system.
Any ideas or hints for things to try?