Micrologix 1500 Faulting with memory module

apatjr

Member
Join Date
Apr 2008
Location
Houston
Posts
2
We programmed a Micrologix 1500 we had left over. We forgot to insert the memory module. So we powered down, inserted the memory module and powered back up. The controller now has a flashing fault light and we cannot make contact through our programming cable. Any ideas what happened and how to get into the processor so we can clear the fault?

Thanks in advance
 
Did the memory module have a program in it? If so it may have changed the way the comm port(s) are configured.

The ML1500 has a comm toggle button, this will set the comm ports back to their default settings. See PDF
 
Did the memory module have a program in it? If so it may have changed the way the comm port(s) are configured.

The ML1500 has a comm toggle button, this will set the comm ports back to their default settings. See PDF

Or it had no program but the CPU was set to 'read' and read nothing (also loaded nothing) and set the CPU back to default

Did you try to reconfigure your DF1 driver?
 
Or it had no program but the CPU was set to 'read' and read nothing (also loaded nothing) and set the CPU back to default

Did you try to reconfigure your DF1 driver?

+1

Just to add a touch more info;

See attached picture. Disclaimer - snapshot taken from a project for a ML1400, but I *think* they have the same options. Hope this helps.

Capture.PNG
 

Similar Topics

I have been working on this for a while now and I can't seem to get it. I was finally able to view the 1500 on the PanelView under the serial...
Replies
1
Views
78
Hello, I have a 1764 1500 LSP Series A that keeps failing with DTL_E_FAIL I/O error. Searching around it seems there's a weird issue specifically...
Replies
2
Views
103
Good Day i Have Micrologix 1500 LSP, and I want to get data from plc and send it through Modbus RTU slave; I have only ch0 on that plc I Order...
Replies
6
Views
917
Hello folks, Hope everyone is doing fine. I got an OMRON NS10-TVOOB-V2 hmi screen last day and planning to use it with Micrologix 1500. 1. Is...
Replies
4
Views
1,203
Good morning to all, I need to modify an existing PLC MIcrologix 1500 configured with a Modem on Channel 1 (DF1 Full Duplex) and an...
Replies
7
Views
1,425
Back
Top Bottom