hello
i m using siemens count card 6ES7-138-4DA04-0ABO.
I trying to read pulses from mass flow meter .......using TIA PORTAL 11.....
SO PLS help me about this.........
 
Hello and welcome to the forum Pardep.

What is your issue/question exactly?
 
hello boneless
here is a mass flow meter......which is giving pulses. for count those pulses we r using this card. programming software is tia portal 11.
i got a sample programe.......but its not working....

Configuration Using STEP7 and HWCONFIG
You begin by adapting the hardware configuration of your existing ET 200S station.
Open the relevant project in SIMATIC Manager.
Call the HWCONFIG configuration table in your project.
Select the 1Count 24V/100kHz entry from the hardware catalog. The number 6ES7 138-4DA04-0AB0 C appears in the information text. Drag the entry to the slot at which you have installed your 1Count24V/100kHz.
By double-clicking on this number, call up the register properties – 1Count24V/100kHz (R – S slot number).
On the Addresses tab you will find the addresses of the slot to which you have
dragged the 1Count24V/100kHz. Make a note of these addresses for subsequent programming.
On the Parameters tab you will find the default settings for the 1Count24V/100kHz.
Leave the default settings unchanged.
Save and compile your configuration, and download the configuration in STOP mode of the CPU by choosing PLC → Download to Module.
Integration in the User Program (not for modified user data interface)
Create block FC101 and integrate it in your control program (in OB1, for example).
This block requires the data block DB1 with a length of 16 bytes. The start address of the module in the following example is 256.
STL Description
Block: FC101
Network 1: Presettings
L 0 //Delete control bits
T DB1.DBD0
T DB1.DBD4
SET
S DB1.DBX4.0 //Open SW-gate
Network 2: Write to the control interface
L DB1.DBD0
T PQD 256 //Write 8 bytes to the 1Count24V/100kHz
L DB1.DBD4 //Configured start adress of the outputs
T PQD 260
Network 3: Read from the feedback interface
L PID 256
T DB1.DBD8 //Read 8 bytes from the 1Count24V/100kHz
L PID 260 //Configured start address of the inputs
T DB1.DBD12
 
Hello Pardep;
You say "but it is not working"...
What are the symptoms, active LEDs, error messages ... that you see when you try to compile and download this program to your CPU?
Hope this helps,
Daniel Chartier
 
dear dchartier
i m doing this program trough remotely(Team viewer) ...so i cant see the led status......but there is no error when i compile the program n download the program in cpu.......it is my first time on this card......sir if u have any program pls send me.......

thanks
 
Once you download the program. Go online and check diagnostics of the CPU. It will tell you if there are errors (or if it is even running).

Also error codes from your counter function blocks could be helpful. I am not very fluent in counters and the like, but I know mr. Chartier is :).
 

Similar Topics

Hi Guys, I have a 1769-L24-QBFCB1 that has the OK light flashing on the embedded counter module. The manual states it is a resettable fault, but...
Replies
0
Views
98
Hey Everyone, After reading a lot on this forum and elsewhere I see not many are fond of the 1794-VHSC module. I can see to a degree as I was...
Replies
3
Views
146
Hello Folks, Has anyone configured a Momentum high speed counter on Unity 13.1. We need the wiring diagram for Momentum High speed counter and...
Replies
0
Views
73
Hi all, I am working with an incremental encoder (ABZ signals, 360 ppr (so 1440 counts per rev)) to replace the existing "manual" encoder wheel I...
Replies
51
Views
2,559
Hi y'all Just a quick question for using Rslogix 5000 I'm using a counter up bit with an analog signal (0-10V). When 10V is measured, counter...
Replies
5
Views
229
Back
Top Bottom