Hello Everyone,

I am working on an already existing project updating new equipments installed.
I have no prior experience in this field but I do not want to give up without a fight.
The project has genies all I did was copy the genies and updating the cluster and tags of the equipment as per the PLC.
After compiling I tried running but I get an error every time I click on my equipment. The other equipments give a popup window such thst you can either open or close the equipment but my error is as on the picture shown

View attachment image1.jpg

Please Help
 
First please upload your image again. If you have older project you should backup to .ctz files first then restore at your computer. For Genies when you copy it to Graphic Builder when you completed edit you should select Update Pages and compile to your project. Then run to check that it works properly or not.

Please check these links below about Genies and Super Genies (It is in Thai Language please use google translate to solve it)

https://scadaskill.blogspot.com/2017/01/learn-vijeo-citect-scada-from-scratch-part-015-genies.html

https://scadaskill.blogspot.com/2017/01/learn-vijeo-citect-scada-from-scratch-part-016-super-genies.html
 
First please upload your image again. If you have older project you should backup to .ctz files first then restore at your computer. For Genies when you copy it to Graphic Builder when you completed edit you should select Update Pages and compile to your project. Then run to check that it works properly or not.

Please check these links below about Genies and Super Genies (It is in Thai Language please use google translate to solve it)

https://scadaskill.blogspot.com/2017/01/learn-vijeo-citect-scada-from-scratch-part-015-genies.html

https://scadaskill.blogspot.com/2017/01/learn-vijeo-citect-scada-from-scratch-part-016-super-genies.html


https://mail.google.com/mail/u/0?ui...749428&th=166734df337c53b4&view=att&disp=safe
 
View attachment 49195

trying for the last time before sending you google drive link

Now I can see your image. I think it miss some equipment option. You should go to Citect Project Editor and select Equipment then check at equipment PS1 that have device MOV2165 or not. If it exist then go to variable tag and check that there are PS1.MOV2165 tag or not.
 
Now I can see your image. I think it miss some equipment option. You should go to Citect Project Editor and select Equipment then check at equipment PS1 that have device MOV2165 or not. If it exist then go to variable tag and check that there are PS1.MOV2165 tag or not.

The PS1 is the cluster and Tag Name is MOV2165
MOV2165 is a motorized valve
I have created following variable tags and trend tags

1. No_Operations Tag
2. Status_Tag
3. Command Tag
4. ComandRemote on HMI Tag

All have given address according to the PLC

Appreciate Your Help
 
The PS1 is the cluster and Tag Name is MOV2165
MOV2165 is a motorized valve
I have created following variable tags and trend tags

1. No_Operations Tag
2. Status_Tag
3. Command Tag
4. ComandRemote on HMI Tag

All have given address according to the PLC

Appreciate Your Help

If you had .ctz backup project. You should restore on new project and edit it.
Please show variable tags setting of MOV2165.
 

Similar Topics

I have DI module ICPCon M7024UD connect to my pc using COM3 MODBUS RTU and also RHT sensors are using MODBUS TCPIP.. The problem is, it cannot...
Replies
9
Views
1,620
Hello guys, I am new in this PLC programming and currently working in a smart chiller system that used Vijeo Citect 7.4. Now, my supervisor ask...
Replies
0
Views
594
Hello I created a program in unity pro and HMI local on Vijeo Citect and communication between them realize by OFS OPC FACTORY . before the...
Replies
4
Views
1,930
Hi, I am new to Vijeo Citect.I have few problems need someone to help, hopefully can solve the problem and get the answer. I using 1 Server and 1...
Replies
2
Views
4,176
Back
Top Bottom