Hi, I hope that some-one can help me wisth this problem.

The situation is that I have a GE Fanuc 90-30 PLC linked to two Redlion G303 HMIs, via a RTU modbus, which controls to two Hydro-electric turbines.

They are set up with the PLC and one of the G303 HMIs are set as slaves, and the remaining G303 HMI is the Master.

The G303 Master <-> PLC communication is fine, and for the most part the G303 Slave <-> PLC (via G303 Master) communication is OK.

However, if the G303 Slave is powered down & up, or its program is updated, when go to any of the screens to modify register values in the PLC, all of the registers that the G303 Slave has access to are reset back to zero, which is a big problem.

Can anyone suggest a solution?
 
Things have finally progressed, so that I am now commissioning the site.

But something has gone strange, and I am now unable to read from the slave HMI to either the master HMI, or use gateway block (in Master HMI) to transfer the data from the slave HMI to the slave PLC.

This was working at the panel test last year, but not now????

HELP!!!! This is a serious problem, as we are in the middle of commissioning, and need this facility.

Can anyone help????
 
Just a update for every-one.

With many thanks to DanYost, who spotted in the programs, that the Master HMI was asking for information in addresses that didn't exist in the slave HMI.

Result: The comms was all fouled up.

Thanks again.
 

Similar Topics

Hi, i am having an issue with a RedLion G303 when i manually assign an IP/subnet to the ethernet interface. If i manually set up the G303 with...
Replies
6
Views
3,344
Hi, I have a Redlion G303 HMI and wish to read various input status' from an alarm unit that sends the data via Modbus. I have only worked with...
Replies
1
Views
1,829
I have a RedLion G303 that I’m feeding ASCII string data from a weight scale. String is: <STX><Signed DATA><sp><lb/kg><CR> <STX> =...
Replies
8
Views
2,888
Hi, we have a G303 we are hoping to use to connect to an Allen Bradley SLC 5/02 via DH485 we have written most to the database (attached) the...
Replies
12
Views
2,730
Hi we have a Redlion G303 display and need it to comunicate with a Allen bradley (SLC 5/02 or SLC 5/04) can it do this and also how do we set up...
Replies
38
Views
7,333
Back
Top Bottom