I tried to find some information using the search engine and I couldn't find anything helpful, so I'll post this here.
I've been assigned to a new platform and one of the first things brought to my attention was a series of "nuisance" alarms on the alarm screen. Digging into the problem, the other SCADA tech and I have found that there are two alarm pages, one set up as an alarm summary page, and one set up as an alarm history page. I'm digging it so far.
However, what happens is that the alarm summary page "acts" like it is displaying alarm history. It keeps the alarms for days. Meanwhile, the alarm history page starts dumping alarms after a minute or so.
I've checked the settings on the pages and they seem to be setup properly. If I go to the Alarm Summary page and doubleclick on it to pull up the alarm configuration box, it is configured to pull up a summary query of all alarms on \InTouch!$System.
The history page is set up to do a history query of all alarms within \InTouch!$System.
There is also a series of scripts written for both pages. I will include a copy of them below:
This is the script for history page.
Old_Screen_Num = Screen_Num;
Screen_Num = 9;
almSetQueryByName( "Alarm_Hist", "default_A_Hist");
Alm_View = 1;
SelectionType = 1;
{IF Alm_View ==1 THEN
Alm_from_Priority =500;
Alm_to_Priority = 979;
ELSE
IF Alm_View ==2 THEN
Alm_from_Priority =500;
Alm_to_Priority = 509;
ELSE
IF Alm_View ==3 THEN
Alm_from_Priority =600;
Alm_to_Priority = 609;
ELSE
IF Alm_View ==4 THEN
Alm_from_Priority =700;
Alm_to_Priority = 799;
ELSE
IF Alm_View ==5 THEN
Alm_from_Priority = 610;
Alm_to_Priority = 611;
ELSE
IF Alm_View ==6 THEN
Alm_from_Priority = 800;
Alm_to_Priority = 809;
ELSE
IF Alm_View ==7 THEN
Alm_from_Priority = 900;
Alm_to_Priority = 910;
ELSE
IF Alm_View ==8 THEN
Alm_from_Priority = 810;
Alm_to_Priority = 811;
ELSE
IF Alm_View ==9 THEN
Alm_from_Priority = 920;
Alm_to_Priority = 939;
ELSE
IF Alm_View ==10 THEN
Alm_from_Priority = 940;
Alm_to_Priority = 959;
ELSE
IF Alm_View ==11 THEN
Alm_from_Priority = 510;
Alm_to_Priority = 519;
ELSE
IF Alm_View ==12 THEN
Alm_from_Priority = 520;
Alm_to_Priority = 529;
ENDIF;
ENDIF;
ENDIF;
ENDIF;
ENDIF;
ENDIF;
ENDIF;
ENDIF;
ENDIF;
ENDIF;
ENDIF;
ENDIF;
ENDIF;}
This is the script for the summary page.
Old_Screen_Num = Screen_Num;
Screen_Num = 10;
almSetQueryByName( "Alarm_", "default_A");
Alm_View = 1;
SelectionType = 2;
{IF Alm_View ==1 THEN
Alm_from_Priority =500;
Alm_to_Priority = 979;
ELSE
IF Alm_View ==2 THEN
Alm_from_Priority =500;
Alm_to_Priority = 509;
ELSE
IF Alm_View ==3 THEN
Alm_from_Priority =600;
Alm_to_Priority = 609;
ELSE
IF Alm_View ==4 THEN
Alm_from_Priority =700;
Alm_to_Priority = 799;
ELSE
IF Alm_View ==5 THEN
Alm_from_Priority = 610;
Alm_to_Priority = 611;
ELSE
IF Alm_View ==6 THEN
Alm_from_Priority = 800;
Alm_to_Priority = 809;
ELSE
IF Alm_View ==7 THEN
Alm_from_Priority = 900;
Alm_to_Priority = 910;
ELSE
IF Alm_View ==8 THEN
Alm_from_Priority = 810;
Alm_to_Priority = 811;
ELSE
IF Alm_View ==9 THEN
Alm_from_Priority = 920;
Alm_to_Priority = 939;
ELSE
IF Alm_View ==10 THEN
Alm_from_Priority = 940;
Alm_to_Priority = 959;
ELSE
IF Alm_View ==11 THEN
Alm_from_Priority = 510;
Alm_to_Priority = 519;
ELSE
IF Alm_View ==12 THEN
Alm_from_Priority = 520;
Alm_to_Priority = 529;
ENDIF;
ENDIF;
ENDIF;
ENDIF;
ENDIF;
ENDIF;
ENDIF;
ENDIF;
ENDIF;
ENDIF;
ENDIF;
ENDIF;
ENDIF;}
The original programmer used the priorities as a way to subdivide alarm groups so he could filter out alarms by section. Pretty interesting notion and it seems to work well, but it seems irrelevant to me in terms of fixing this problem.
Basically, nothing I've done seems to make any difference. Am I completely misunderstanding what the difference between history and summary queries is? I would think the history query and page would show a long term historical view, whereas the summary page would basically be an instantaneous snapshot of what is happening right now, but this set up is acting exactly the opposite way. Rather than going on endlessly with information that is of no use, I'll give you guys the opportunity to look at what I've got and come back with any questions for clarification. Thank you for your help,
Mark
I've been assigned to a new platform and one of the first things brought to my attention was a series of "nuisance" alarms on the alarm screen. Digging into the problem, the other SCADA tech and I have found that there are two alarm pages, one set up as an alarm summary page, and one set up as an alarm history page. I'm digging it so far.
However, what happens is that the alarm summary page "acts" like it is displaying alarm history. It keeps the alarms for days. Meanwhile, the alarm history page starts dumping alarms after a minute or so.
I've checked the settings on the pages and they seem to be setup properly. If I go to the Alarm Summary page and doubleclick on it to pull up the alarm configuration box, it is configured to pull up a summary query of all alarms on \InTouch!$System.
The history page is set up to do a history query of all alarms within \InTouch!$System.
There is also a series of scripts written for both pages. I will include a copy of them below:
This is the script for history page.
Old_Screen_Num = Screen_Num;
Screen_Num = 9;
almSetQueryByName( "Alarm_Hist", "default_A_Hist");
Alm_View = 1;
SelectionType = 1;
{IF Alm_View ==1 THEN
Alm_from_Priority =500;
Alm_to_Priority = 979;
ELSE
IF Alm_View ==2 THEN
Alm_from_Priority =500;
Alm_to_Priority = 509;
ELSE
IF Alm_View ==3 THEN
Alm_from_Priority =600;
Alm_to_Priority = 609;
ELSE
IF Alm_View ==4 THEN
Alm_from_Priority =700;
Alm_to_Priority = 799;
ELSE
IF Alm_View ==5 THEN
Alm_from_Priority = 610;
Alm_to_Priority = 611;
ELSE
IF Alm_View ==6 THEN
Alm_from_Priority = 800;
Alm_to_Priority = 809;
ELSE
IF Alm_View ==7 THEN
Alm_from_Priority = 900;
Alm_to_Priority = 910;
ELSE
IF Alm_View ==8 THEN
Alm_from_Priority = 810;
Alm_to_Priority = 811;
ELSE
IF Alm_View ==9 THEN
Alm_from_Priority = 920;
Alm_to_Priority = 939;
ELSE
IF Alm_View ==10 THEN
Alm_from_Priority = 940;
Alm_to_Priority = 959;
ELSE
IF Alm_View ==11 THEN
Alm_from_Priority = 510;
Alm_to_Priority = 519;
ELSE
IF Alm_View ==12 THEN
Alm_from_Priority = 520;
Alm_to_Priority = 529;
ENDIF;
ENDIF;
ENDIF;
ENDIF;
ENDIF;
ENDIF;
ENDIF;
ENDIF;
ENDIF;
ENDIF;
ENDIF;
ENDIF;
ENDIF;}
This is the script for the summary page.
Old_Screen_Num = Screen_Num;
Screen_Num = 10;
almSetQueryByName( "Alarm_", "default_A");
Alm_View = 1;
SelectionType = 2;
{IF Alm_View ==1 THEN
Alm_from_Priority =500;
Alm_to_Priority = 979;
ELSE
IF Alm_View ==2 THEN
Alm_from_Priority =500;
Alm_to_Priority = 509;
ELSE
IF Alm_View ==3 THEN
Alm_from_Priority =600;
Alm_to_Priority = 609;
ELSE
IF Alm_View ==4 THEN
Alm_from_Priority =700;
Alm_to_Priority = 799;
ELSE
IF Alm_View ==5 THEN
Alm_from_Priority = 610;
Alm_to_Priority = 611;
ELSE
IF Alm_View ==6 THEN
Alm_from_Priority = 800;
Alm_to_Priority = 809;
ELSE
IF Alm_View ==7 THEN
Alm_from_Priority = 900;
Alm_to_Priority = 910;
ELSE
IF Alm_View ==8 THEN
Alm_from_Priority = 810;
Alm_to_Priority = 811;
ELSE
IF Alm_View ==9 THEN
Alm_from_Priority = 920;
Alm_to_Priority = 939;
ELSE
IF Alm_View ==10 THEN
Alm_from_Priority = 940;
Alm_to_Priority = 959;
ELSE
IF Alm_View ==11 THEN
Alm_from_Priority = 510;
Alm_to_Priority = 519;
ELSE
IF Alm_View ==12 THEN
Alm_from_Priority = 520;
Alm_to_Priority = 529;
ENDIF;
ENDIF;
ENDIF;
ENDIF;
ENDIF;
ENDIF;
ENDIF;
ENDIF;
ENDIF;
ENDIF;
ENDIF;
ENDIF;
ENDIF;}
The original programmer used the priorities as a way to subdivide alarm groups so he could filter out alarms by section. Pretty interesting notion and it seems to work well, but it seems irrelevant to me in terms of fixing this problem.
Basically, nothing I've done seems to make any difference. Am I completely misunderstanding what the difference between history and summary queries is? I would think the history query and page would show a long term historical view, whereas the summary page would basically be an instantaneous snapshot of what is happening right now, but this set up is acting exactly the opposite way. Rather than going on endlessly with information that is of no use, I'll give you guys the opportunity to look at what I've got and come back with any questions for clarification. Thank you for your help,
Mark