SLC 5/05 RIO 1747-SN and 1747-ASB Configuration Questions

reese006

Member
Join Date
Sep 2008
Location
Birmingham, AL
Posts
21
OK I have a question on RIO configuration and how to access my analog data. My question has to do with the BTR and BTW Buffer File. I am not onsite yet but wanted to try and get my ducks in a row before I head out this week. The Local Rack has been in place for many years and they have added the Remote Rack. Here is the configuration of what I was planning on. Card locations on the RIO rack not set in stone so if you guys think they need to be moved around speak up. Please note I am trying to make this as simple as possible. The odds of adding anything else to the RIO rack are very slim.

Here is my setup:
Local Rack 10-Slot Configuration
0. 1747-L553B/C
1. 1746-NI16I
2. 1746-NI16I
3. 1746-NO4I
4. 1746-NO4I
5. 1746-IB16
6. 1746-OW16
7. 1746-OW16
8. 1746-IB16
9. 1747-SN

Remote Rack 10-Slot Configuration
0. 1747-ASB
1. 1746-IB8
2. 1746-OW8
3. 1746-NT4
4. 1746-NI16I
5. 1746-NO4I
6. Blank
7. Blank
8. Blank
9. Blank

1747-SN Scanner Configuration
Max Input Words: 32
Max Output Words: 32
Scanned Input Words: 32
Scanned Output Words: 32
Interrupt Service Routine#0
M0 Length: 3300
M1 Length: 3300
G File Length: 3

G File Configuration:
Logical Rack 0: Group 0: Full Rack

1747-ASB Dip Switches
SW1
1 ON
2 ON
3 ON
4 ON
5 ON
6 ON
7 ON
8 ON

SW2
1 ON
2 ON
3 ON
4 ON
5 ON
6 ON
7 OFF
8 ON

SW3
1 ON
2 ON
3 ON
4 ON
5 ON
6 OFF
7 OFF
8 ON

I think I am good on the RIO DI and DO card and there inputs and outputs. All those look like they will come over into my I:9 and O:9 Data Files correct? I know once I get one of the Analog cards the others should fall in to place. Ok here is my question say for the Thermocouple Card that is in the remote rack slot 3. If I needed to configure Channel 0 on the thermo card would my BTW instruction look like:
Block Transfer Write
Rack: 0
Group: 2
Slot: 0
Control Block: N99:0
Data File: N100:0
Buffer File: M0:9.100
Requested Word Count: 1
Where the control block N99:0 is the 3 words for the BTW structure and N100:0 is my configuration word for Channel 0.

And if I wanted to read Channel 0 on the Thermo Card my BTR would look like:
Block Transfer Read
Rack: 0
Group: 2
Slot: 0
Control Block: N99:10
Data File: N101:0
Buffer File: M1:9.108
Requested Word Count: 1
Where the control block N99:10 is the 3 words for the BTR structure and N101:0 is data from Channel 0.

I have now realized how spoiled I have been with Control Logix.
 
The one thing that jumps out at me is the Buffer File numbers. You need to use increments of 100 for you buffer files, starting at 100, and they each must be unique.

So, for the BTR, change it to M1:9.200.

I haven't had time to look into your dipswitch settings but the rest of it looks okay...
 

Similar Topics

I hope somebody can guide me on right direction. I’m trying to setup for the first time a RIO PV550, 1747 SN B and SLC 5/04 OS401 B. For almost...
Replies
0
Views
5,620
I’ve searched the internet for answers on how to do this. But I’m in need of some help. I have a slc 500 connected to a RIO. There are two racks...
Replies
6
Views
1,107
I am getting an error on my 1747 - ASB that says NOC. I looked this up in the manual and all it says is no communication. Which I knew that lol...