Connecting PG to S5

Grzesiuk

Member
Join Date
Dec 2018
Location
Ukraine
Posts
24
Hello!
I'm facing a problem with connecting PG to S5. My PG is 6es7712-0aa00-0ag5 and S5 has CPU 115U. I receive System message no.:0334. You can see on screenshoot my wiring with RS232 25 pin sub-d and 15 pin sub-d.
http://i67.tinypic.com/sbsc5w.jpg

I was also trying to choose COM1: Standard and COM1, but without any result. I've checked also my COM settings which are: 9600 bps, 8 Data bits, None Parity, 1 Stop bits, None flow control and Receive Buffer/Transmit Buffer are set to minimum. Could you provide me with information, what I'm doing wrong in order to connect with S5? I can guess there is something wrong with the wiring, but I would be grateful for information, which cables should I use.
Thank you!
 
The Field-PG M has an integrated TTY adapter in the 25-pin COM-1 port.
Here is the manual: https://support.industry.siemens.com/cs/de/en/view/21743385

You need the cable 6ES5734-2BD20 to connect this directly to the PG-port on the CPU.
An RS232 cable with the 25-pin standard connections will not work.
The serial port settings for COM1 are probably irrelevant. The TTY port always uses 9600 baud and cannot be changed.
 
I dont know the use of STEP5 with this PC, but I am guessing that "standard" is the integrated TTY adapter, and "COM1" is with an external RS232/TTY adapter.
So you should probably use the "standard" setting.
 
The Field-PG M has an integrated TTY adapter in the 25-pin COM-1 port.
Here is the manual: https://support.industry.siemens.com/cs/de/en/view/21743385

You need the cable 6ES5734-2BD20 to connect this directly to the PG-port on the CPU.
An RS232 cable with the 25-pin standard connections will not work.
The serial port settings for COM1 are probably irrelevant. The TTY port always uses 9600 baud and cannot be changed.


That is exactly what I needed, thank you for the answer, looks like I have to order a cable :)
 

Similar Topics

Hello, I was looking to store some values from our FactoryTalk Application using Datalog to a MariaDB. I see there is quite a bit of documentation...
Replies
1
Views
37
I haven't encountered problems connecting to a PLC through VM Ware but I am with this particular machine. I'm running Windows 7 on a Windows 10...
Replies
8
Views
167
Hi, I want to build a demo station to test devices and programs and I need some help with it. I want to connect GuardLogix, Piltzmulti and...
Replies
1
Views
134
please using the usb can i assign any ip address that i want ?
Replies
4
Views
145
Hi everyone, I need some help I new with omron plc. I using plc CP1L. When I do the program it's good and the plc is function as program. But when...
Replies
1
Views
83
Back
Top Bottom