TIA Portal v14 cannot go online with S7-1500

doomsword

Member
Join Date
Aug 2016
Location
Zagreb
Posts
201
We have one problem with TIA Portal and S7-1500 PLCs, it is that every while during download we get download to device error and error that 'service is not started'. So far it happened 4 times in ~5 months on one PLC where more than one person is working.

After that we cannot access PLC with TIA Portal, we cannot go online with it. And more, it happens for all who try to access PLC, if someone gets this error communication cannot be established for ANYONE trying to access PLC with TIA Portal.

HMI-PLC communication continues normally, and execution of PLC program is normal. But programmers cannot access PLC until it is completely rebooted, basically we shut it down and restart it.
Putting PLC to stop and run or changing port from which you access and other methods we tried don't work.
Only complete shutdown.

Does anyone have any idea what this problem is? Next time we'll try to screenshot error and send it to Siemens, but it could take some time until we repeat it again.

Does anyone know has this error been already recognized and fixed by Siemens? Is it firmware problem or a bug inside TIA Portal?
 
"It says communication to PLC was lost" have you checked your connection. Maybe you have loose connection. Maybe your Ethernet cabe needs to be replaced.

Have you tried Siemens support?
 
"It says communication to PLC was lost" have you checked your connection. Maybe you have loose connection. Maybe your Ethernet cabe needs to be replaced.

Have you tried Siemens support?


Damn, of course we tried a lot of things, including that one. And this has happened to two different PLCs, on two different switches, in two different countries. But with same project running on both PLCs.
So either something in project is broken, or inside TIA Portal or in firmware on at least two PLCs (probably all PLCs).

We contacted support, hope they'll have some answers. We can't really upgrade firmware, we'd need TIA v15 for that...
 

Similar Topics

Hi everyone. Please help me to upload program from S7-1200 with TIA v14. I created new project, go to Online tab, select Upload devices as new...
Replies
0
Views
1,082
I am beatin gmy head against the wall trying to get my modbus comms working. I have a s7-1200 running tia v14, a cm-1241 comm card. I have...
Replies
22
Views
7,396
I am trying to commission a compressor that is using a s7-1200 to communicate rs485/modbus to a the compressor interface. My rs485 module is a...
Replies
2
Views
1,698
Is it possible to install Siemens Tia Portal V14 on a machine that already has V16 installed? Or do I need to create a virtual machine to install...
Replies
17
Views
8,877
Is anyone know how to change the state of Button and multistate indicator(for Verify changing in color and text) in TIA portal HMI while doing...
Replies
1
Views
1,320
Back
Top Bottom