I have a proface HMI model number pfxsp5b10, it has been damaged somehow and has a blank screen. So I am trying to recover the configuration file from the unit. I am using GP pro x free version, but when I try to transfer the file by lan I get not connected to unit. I have set my pc ip to the same sub net and I can ping the unit successfully. Im wondering does the free version of the software allow you to transfer files from the proface to a pc? Or is there something else wrong? Please see attached pics of screen shots

proface 2.png
 

Attachments

  • proface1.jpg
    157 bytes · Views: 4
What exactly has been damaged: the PFXSP5B10 unit or the actual screen? The unit you mention is so-called "power box" which contains all the smarts and which snaps onto the back of a "dumb" touchscreen.

If it is only the screen that was damaged, can you unsnap the power box and snap it to another Pro-face HMI? The size does not matter: the box should work with any SP5000 series Pro-face touchscreen of any size, although the actual application screens would look different due to different screen resolutions, of course.
 
went through the list, I can ping the unit, I am not getting a firewall pop up but I may try to disable that anyway. I know the ip and it does respond to a ping. thanks for everyone's help.
 

Similar Topics

Hi all, i have several Proface GT2400 terminals and i need to get the software and interface cables and i have several questions. I am assuming...
Replies
3
Views
154
I have followed the videos & still having issues getting the email out. Does anyone have knowledge or has sent an email notification via gp pro ex?
Replies
0
Views
189
Has anyone found a Proface HMI that is compatible with Schneider M172 PLC?
Replies
0
Views
378
Hi, I received the following project from a customer on a QuickPanel Proface 6" that I need to swap to a Siemens Panel. However, I cannot seem to...
Replies
3
Views
316
Does anyone know if is possible to read data out of a ProfaceHMI/PLC into a CompactLogix PLC? I have a bunch of OEM machines on our plant floor...
Replies
2
Views
486
Back
Top Bottom