Hi, I've got a B&R X20CP3584 PLC with an X20IF10G3-1 EtherCAT slave card. I'm trying to connect it to an EtherCAT master device (a KUKA KRC4), but there doesn't seem to be any place for me to set the slave address in Automation Studio. Does anyone know how to do this? Thanks!
 
Not claiming to be an expert on EtherCAT, but I thought that in majority of cases the slave address is set automatically, when the master scans the network.
 
The user "Ladderlogic" is right:

Ethercat Master are able to set the station address during startup.
This has to be made by the master.
This sequence is due to the Ethernet Slave hast an "IN" (IF1) and "OUT" (IF2) connection.


On Basis of the physical order the slave is recognized and identified.
 
Hi, I´ve got B&R PLC X20CP1382 and etherCAT modul X20IF10G3-1 and I need to communicate with Kuka KRC4 via EtherCAT. Is there some procedure how to set up communication in Automation studio 4.3.?
Thank you.
 

Similar Topics

Hi need help why this “failure 5 emergency stop “ appears at every startup in the morning ? Have to shut off main switch at least 10 times on...
Replies
19
Views
213
Omron AD081-V1 Analog Input Card Offset & Gain Adjustment Entering Adjustment Mode 1. Set the input card in adjustment mode (Turn ON Dip SW No-1)...
Replies
0
Views
86
I was loading a program onto an XE1e2 PLC and it got stuck on these two windows and won't progress. It won't let me connect from the PC to reload...
Replies
0
Views
72
Hi all, i have recieved some 4RF Aprisa SR+ ethernet radios from a customer to configure. Issue is that they are used and have non-default...
Replies
0
Views
73
I want to set user security level based on the value of a tag in my PLC called "ActiveUser". That tag will contain the A-P code which we use for...
Replies
6
Views
207
Back
Top Bottom