Old May 25th, 2018, 01:11 PM   #1
Cydog
Member
United States

Cydog is offline
 
Join Date: Feb 2018
Location: Maryland
Posts: 280
PowerFlex 70 - Best way to communicate with , CCW , Drive Executive,etc. ?

Good Afternoon ,

We still have a number of Powerflex 70 drives throughout the plant. Many are being controlled by DeviceNet that I plan on getting rid of. My question is what is the best way to upload and download from a PowerFlex 70 , Drive Executive , CCW , etc. ?

I imagine that there is a modified HIM that allows you to hook up a PowerFlex 70 to your laptop , correct ?

When you upload , I imagine that you upload everything in the drive ?
  Reply With Quote
Old May 25th, 2018, 03:11 PM   #2
dburnum
Member
United States

dburnum is offline
 
dburnum's Avatar
 
Join Date: Oct 2008
Location: SW Kansas
Posts: 160
My facility has about 75 VFDs in it...all AB PowerFlex drives, as that is what we can get quick support with. We do have a few older 1336 drives, but most are PF70, with some newer additions of PF753 and PF525. I used to use Drive Executive, but some of the newer 753s I put DriveLogix into, so have now switched all my drives to CCW. It's not bad, and for the most part is like Drive Executive, but I can place all my drives into a single CCW file, or break up the CCW files by areas in the facility. I keep that file in cloud storage, now, so that if I ever have a corruption issue, I can recover it quickly and painlessly. You should be able to communicate individually with any PowerFlex Drive via a 1203-USB Anaconda device. It still requires RSLINX to communicate via the serial physical connection.
  Reply With Quote
Old May 25th, 2018, 05:45 PM   #3
thingstodo
Member
Canada

thingstodo is offline
 
Join Date: Feb 2012
Location: Saskatoon
Posts: 498
Quote:
Originally Posted by Cydog View Post
Good Afternoon ,

We still have a number of Powerflex 70 drives throughout the plant. Many are being controlled by DeviceNet that I plan on getting rid of. My question is what is the best way to upload and download from a PowerFlex 70 , Drive Executive , CCW , etc. ?

I imagine that there is a modified HIM that allows you to hook up a PowerFlex 70 to your laptop , correct ?

When you upload , I imagine that you upload everything in the drive ?
It's been a while .. but Drive Executive used to ask if you wanted to upload all parameters or only those changed from default. Upload all.

When downloading, it is important to make sure that the firmware is correct. If major versions are the same, things are generally OK. If you major revisions are not the same, it will ask you to confirm version change and then do it. I have run into some gotchas in this process.

If you are planning to download to the same drives after replacing 20-comm-D with 20-comm-E ... you will be fine.

We download/upload through devicenet or controlnet or ethernet, using RSLinx and drive executive. To use a new 20-comm-e you will need to set up the ethernet address with the HIM after the powerflex is powered up.

I am not aware of a HIM that connects to a laptop. The 1203-USB would also be my choice for direct connection.
  Reply With Quote
Old May 26th, 2018, 10:28 PM   #4
jraef
Member
United States

jraef is offline
 
jraef's Avatar
 
Join Date: May 2006
Location: Northern California
Posts: 2,104
CCW is the way forward. Drive Executive is still active, but is not being developed further so as time goes by it will not support newer firmware revs etc.

And yes, the 1203-USB is the way to connect, at least until you change to Ethernet.
  Reply With Quote
Old May 27th, 2018, 04:37 AM   #5
iraiam
Member
United States

iraiam is offline
 
Join Date: Jul 2011
Location: Right here
Posts: 146
I use CCW, and the the Allen Bradley 1203-USB interface. I support various PowerFlex drive models with this setup. Including Powerflex 70 with Device Net as you describe.
  Reply With Quote
Old May 27th, 2018, 09:30 AM   #6
Cydog
Member
United States

Cydog is offline
 
Join Date: Feb 2018
Location: Maryland
Posts: 280
Thanks for your advice . About the 1203-USB , the only connection point I see for communication is where the HIM connects . Is there another port that I'm missing .

Thanks so much for you help .
  Reply With Quote
Old May 27th, 2018, 10:02 AM   #7
iraiam
Member
United States

iraiam is offline
 
Join Date: Jul 2011
Location: Right here
Posts: 146
Quote:
Originally Posted by Cydog View Post
Thanks for your advice . About the 1203-USB , the only connection point I see for communication is where the HIM connects . Is there another port that I'm missing .

Thanks so much for you help .
Yes, the PowerFlex 70 has a ScanPort (Round 8-pin), Or possibly a DSI port (RJ45). The 1203-USB comes with a cable to make the connection to either type. I think you will likely find the 8 pin round connector on a 70.

I have also seen these connectors hidden behind covers, say on a NEMA rated drive. That is the drive itself is NEMA rated to be installed stand alone outside of a cabinet.

Last edited by iraiam; May 27th, 2018 at 10:12 AM.
  Reply With Quote
Old May 28th, 2018, 12:48 AM   #8
alan_505
Lifetime Supporting Member
Australia

alan_505 is offline
 
Join Date: Feb 2007
Location: Melbourne,Victoria,Australia
Posts: 732
All the 7 (70,700, 700H, 700S, 7000, 753, 755) series drives have a ScanPort (8 pin miniDin socket), port location varies by drive size and type.

All the 4 (4, 4M, 40, 400) and 5 (52x) series drives have the DSI port (RJ45 style socket).

Alan.
  Reply With Quote
Old May 13th, 2022, 02:37 AM   #9
Tresco-oz
Member
Australia

Tresco-oz is offline
 
Tresco-oz's Avatar
 
Join Date: Oct 2005
Location: Melbourne
Posts: 46
Quote:
Originally Posted by alan_505 View Post
All the 7 (70,700, 700H, 700S, 7000, 753, 755) series drives have a ScanPort (8 pin miniDin socket), port location varies by drive size and type.

All the 4 (4, 4M, 40, 400) and 5 (52x) series drives have the DSI port (RJ45 style socket).

Alan.
Hi Alan - hoping I can pick your brain a little as you seem to know the AB PowerFlex units.

My client has a model 700 (20BC105A0AYNANC0)

Do you know if these have a ScanPort? I took the front cover off but couldn't see one.

regards, Phil (also in Melbourne)
Attached Images
File Type: jpg 20220511_100241x.jpg (123.4 KB, 37 views)
__________________
Phil..
  Reply With Quote
Old May 13th, 2022, 06:43 AM   #10
Robobob
Lifetime Supporting Member
United States

Robobob is offline
 
Robobob's Avatar
 
Join Date: Apr 2004
Location: Toledo
Posts: 259
Look at the User manual page 101 Appendix B.
20B-UM002G-EN-P
https://literature.rockwellautomatio...m002_-en-p.pdf
You will see all of the ports by frame size.
  Reply With Quote
Old May 14th, 2022, 11:26 PM   #11
alan_505
Lifetime Supporting Member
Australia

alan_505 is offline
 
Join Date: Feb 2007
Location: Melbourne,Victoria,Australia
Posts: 732
Quote:
Originally Posted by Tresco-oz View Post
Hi Alan - hoping I can pick your brain a little as you seem to know the AB PowerFlex units.

My client has a model 700 (20BC105A0AYNANC0)

Do you know if these have a ScanPort? I took the front cover off but couldn't see one.

regards, Phil (also in Melbourne)

See the black cable coming out of the black cover, part way down on the left. If you follow that cable it will take you to the scanport.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Lost comms using CCW for PowerFlex 255.255.255.0 LIVE PLC Questions And Answers 0 August 12th, 2014 01:25 PM
Mapping of Status/Feedback,Reference/command of a powerflex 70 drive srv LIVE PLC Questions And Answers 6 October 16th, 2011 04:54 AM
Communicate with a Powerflex 70 AC Drive through Ethernet ip Instrumentation Stud LIVE PLC Questions And Answers 11 June 15th, 2010 10:06 AM
OT: PowerFlex 70 Torque Variation kamenges LIVE PLC Questions And Answers 27 April 9th, 2010 02:13 PM
Powerflex 70 20-comm-R DPI intermittant failure robertmee LIVE PLC Questions And Answers 9 March 20th, 2008 03:25 PM


All times are GMT -4. The time now is 02:55 PM.


.