Driver selection for AB SLC 500 5/05 Controller

Hello, I'm trying to figure out how to communicate with this controller. I replaced it, and need to program it. The Ethernet LED is lit.
I have RS Logix500, RS Linx and RS Enterprise. The program says COM:0 Port 7 is in conflict and another driver is in error.
I hope I'm explaining this correctly.
Thanks
  Reply With Quote
Old May 12th, 2022, 01:45 PM   #2
parky
Member
United Kingdom

parky is offline
 
parky's Avatar
 
Join Date: Oct 2004
Location: Midlands
Posts: 4,928
What operating system do you have i.e. win7,10 etc. the 505 also has an Ethernet port have you tried connecting with that, some years since I used AB so cannot remember how to select the driver.
  Reply With Quote
Old May 12th, 2022, 01:49 PM   #3
klmfdc
Member
United States

klmfdc is offline
 
Join Date: Jan 2022
Location: Miami
Posts: 5
1747-l552 c

I forgot to add it's a 1747-L552 C FRN 10+
  Reply With Quote
Old May 12th, 2022, 01:51 PM   #4
klmfdc
Member
United States

klmfdc is offline
 
Join Date: Jan 2022
Location: Miami
Posts: 5
I have windows XP. It has a Ethernet RJ45 port and an RS232
  Reply With Quote
Old May 12th, 2022, 02:00 PM   #5
geniusintraining
Lifetime Supporting Member + Moderator
United States

geniusintraining is offline
 
geniusintraining's Avatar
 
Join Date: Jun 2005
Location: SC
Posts: 8,105
Do you have a 1747-CP3 or Null modem/cross over cable? if yes you can download via the DB9 port, if not you will need to get the IP address in the PLC via flash or Bootp using the Ethernet port
__________________
www.PLCCable.com PLC Communication Cables, PLC Trainers, MicroLogix, ControlLogix, Siemens, Allen Bradley and more...OEM and aftermarket supplies... Aftermarket 1784-U2DHP Allen Bradley USB to DH+, new USB to 485 modbus
  Reply With Quote
Old May 12th, 2022, 04:14 PM   #6
I_Automation
Lifetime Supporting Member
United States

I_Automation is offline
 
I_Automation's Avatar
 
Join Date: Jun 2020
Location: Detroit, Michigan USA
Posts: 1,296
The serial port on a SLC can be changed from RS-232 (DF-1) to DH-485 (UIC needed) if it has a HMI that requires it. I have found systems that didn't have a HMI set to this just because the programmer did. It can also be set to ASCII that can not be used to program through.



If you plug a CAT5 cable directly from the PC to the 5/05 it has to be a cross-over cable or run through a switch that automatically crosses over signals as needed.


Newer 5/05's can be seen using the ETHIP driver that searches and finds anything it can. Older ones had to use the ETH driver that you had to program in the IP address.


Plus in Network Adapter Settings in the properties of your Ethernet adapter you have to set the PC IP address in the same family as the PLC.
__________________
ivanovaautomation.com


Some Jobs Are Best Started With A Sawzall And A Dumpster On Castors
  Reply With Quote
Old May 12th, 2022, 04:31 PM   #7
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 17,101
Since you have replaced the controller, the new one is either in out-of-the-box condition and needs to have an IP address assigned, or it has an unknown IP address.

You can generally connect to it over Ethernet, or via the serial port, whose settings ought to be at the default 19200 baud, 8/N/1 framing, CRC error checking, and DF1 Full Duplex protocol.

You do need some basic Ethernet and TCP/IP networking experience to set up these controllers. No great IT skills, but the basics to understand cables and switches and IP addresses.

The "ETH" LED on the controller will be solid green if it has an IP address and is connected to a switch. If it is set for DHCP or BOOTP, it will make two quick blinks every 30 seconds or so when it transmits a DHCP/BOOTP request.

Because yours is a Series C FRN10+, it supports the modern "EtherNet/IP" driver in RSLinx Classic, which automatically browses the local IP subnet of the network adapter you configure it to use.

When I get one of these controllers out of the box, I connect it to a small dedicated network where my PC is set for 192.168.1.x and run the Rockwell BOOTP/DHCP Server Utility, and browse with RSLinx Classic to see if a commonly-configured address shows up.

There are more sophisticated ways to learn the IP address (do you know how to use Wireshark ?), or we can walk you through the COM port settings of your serial port and the simple null-modem serial connection.

Last edited by Ken Roach; May 12th, 2022 at 04:37 PM.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
SLC 5/05 controlling Powerflex 525 drives over Ethernet ??? sparky mark 9876 LIVE PLC Questions And Answers 6 November 30th, 2016 01:45 PM
SLC 5/05, RSLogix 500, and testing sthays10 LIVE PLC Questions And Answers 19 July 19th, 2013 04:49 PM
SLC 500 CPU Fault / Faulty Output DmpTheKiller LIVE PLC Questions And Answers 4 March 28th, 2012 09:49 PM
serial connection between panelview1000, plc program, ethernet, slc 5/05 controller kasongomoma LIVE PLC Questions And Answers 4 July 5th, 2007 07:19 PM
SLC 500 -1747-L20 AB Fixed Controller Guide nurul LIVE PLC Questions And Answers 8 December 19th, 2005 04:51 PM


All times are GMT -4. The time now is 09:30 AM.


.