Old April 21st, 2014, 07:25 AM   #1
geoplc
Member
United States

geoplc is offline
 
Join Date: Oct 2006
Location: PAinesville OH
Posts: 123
Abb acs800 replace fan

anyone KNOW THE MAINT CODE TO RESET THE "REPLACE FAN" HOURS RUN REGISTER IN ACS800 DRIVE. DID IT FEW YEARS BACK BUT CANT REMEMBER.
  Reply With Quote
Old April 21st, 2014, 07:39 AM   #2
osmanmom
Member
Malaysia

osmanmom is offline
 
Join Date: Mar 2014
Location: JOHOR
Posts: 1,455
01.44-16.12
  Reply With Quote
Old April 21st, 2014, 09:20 AM   #3
geoplc
Member
United States

geoplc is offline
 
Join Date: Oct 2006
Location: PAinesville OH
Posts: 123
Ok Im a little rusty. I know 1.44 is the fault code for the fan hour limit, but dont remember the significance of 16.12 and how I went about resetting it.
  Reply With Quote
Old April 21st, 2014, 09:27 AM   #4
osmanmom
Member
Malaysia

osmanmom is offline
 
Join Date: Mar 2014
Location: JOHOR
Posts: 1,455
Abc
Attached Images
File Type: jpg ABC.jpg (21.8 KB, 427 views)
  Reply With Quote
Old April 22nd, 2014, 09:10 AM   #5
geoplc
Member
United States

geoplc is offline
 
Join Date: Oct 2006
Location: PAinesville OH
Posts: 123
Sorry about delay, parameter 16.12 is not accessible on the keypad control, only goes to 16.11. I vaguely remember having to enter a pass code in order to do this. Supposedly it can be reset using drivewindow software which i believe we may still have. Will look into further.
  Reply With Quote
Old April 22nd, 2014, 09:26 AM   #6
osmanmom
Member
Malaysia

osmanmom is offline
 
Join Date: Mar 2014
Location: JOHOR
Posts: 1,455
Actually it depend your Firmware Manual User,

Inline,Crane,Fan Pump,Extruder,Traverse,IGBT all have their Firmware manual user.

The reset counter will different 16.11-16.12-16.09 base on Firmware manual.

i give you default ACS800 Standard Manual User,

the important thing your Manual User must keep at proper place
  Reply With Quote
Old September 30th, 2015, 08:44 AM   #7
Cphe747
Member
South Africa

Cphe747 is offline
 
Join Date: Sep 2015
Location: Newcastle
Posts: 4
We have some ASC800 drives running on our plant. Some of them have recently gave Alarm Messages on the Control Panel which says: Replace Fan(4280)
I did replace the cooling fan with one from our spare drives.
My problem is the fact that Parameter 16.12 which is used to reset the cooling fan run time counter is not accessible on the control panel.
Is there any method to reset this counter either than using the PC Tool? Is there a pass key or anything that can enable me to view the Parameter 16.12 and 01.44 etc?
  Reply With Quote
Old September 30th, 2015, 05:42 PM   #8
DickDV
Member
United States

DickDV is offline
 
Join Date: May 2002
Location: Kalamazoo MI
Posts: 2,324
Why not give ABB Tech Service a call----800.752.0696 Option 1 and Option 1. Knowledgeable friendly people during business hours in Milwaukee WI and NO CHARGE!
  Reply With Quote
Old October 1st, 2015, 12:37 AM   #9
Cphe747
Member
South Africa

Cphe747 is offline
 
Join Date: Sep 2015
Location: Newcastle
Posts: 4
Quote:
Originally Posted by DickDV View Post
Why not give ABB Tech Service a call----800.752.0696 Option 1 and Option 1. Knowledgeable friendly people during business hours in Milwaukee WI and NO CHARGE!
I will do that, thank you very much
  Reply With Quote
Old November 20th, 2015, 02:44 AM   #10
Wizlock
Member
Norway

Wizlock is offline
 
Join Date: Aug 2014
Location: Western Norway
Posts: 17
Did you get anywhere on this? Having the same problem.
  Reply With Quote
Old November 20th, 2015, 03:10 AM   #11
Cphe747
Member
South Africa

Cphe747 is offline
 
Join Date: Sep 2015
Location: Newcastle
Posts: 4
Quote:
Originally Posted by Wizlock View Post
Did you get anywhere on this? Having the same problem.
Good day, unfortunately I did not come right. I have 20 of these drives. ABB South Africa says I have to send the drives to them or bring their technician onsite which is not practical.
Sorry
  Reply With Quote
Old May 26th, 2016, 08:58 AM   #12
Milspecelectrician
Member
Canada

Milspecelectrician is offline
 
Join Date: May 2016
Location: Canada
Posts: 1
SOLUTION

Okay so I made this account JUST to reply and solve this problem for everyone...
To reset the fan counter do as follows

Go to parameter 16-03
-enter 2303 as passcode
-press enter
-"..." Should appear for a brief moment
Go to parameter 145 (yes 145 now exists, before it only went to 99)
-go to sub-parameter 13 Titled "FAN ON-TIME"
-Press enter
-now you must hold the down arrow until you have brought the hours down to zero. This will take some time as it only decreases in increments of 10, my counter is at 50 000+
-once back to zero press enter. Problem solved, drive should run immediately if being called on to start

Go to parameter 16-03 again
-Press enter
-enter 358 as passcode
-press enter

Now you are done. ACT button out and let fly!



Hope this helps everyone reading this in the future
  Reply With Quote
Old May 26th, 2016, 09:19 AM   #13
Pete.S.
Member
United States

Pete.S. is offline
 
Join Date: Mar 2016
Location: Fl
Posts: 464
Quote:
Originally Posted by Milspecelectrician View Post
SOLUTION

Okay so I made this account JUST to reply and solve this problem for everyone...
To reset the fan counter do as follows

Go to parameter 16-03
-enter 2303 as passcode
-press enter
-"..." Should appear for a brief moment
Go to parameter 145 (yes 145 now exists, before it only went to 99)
-go to sub-parameter 13 Titled "FAN ON-TIME"
-Press enter
-now you must hold the down arrow until you have brought the hours down to zero. This will take some time as it only decreases in increments of 10, my counter is at 50 000+
-once back to zero press enter. Problem solved, drive should run immediately if being called on to start

Go to parameter 16-03 again
-Press enter
-enter 358 as passcode
-press enter

Now you are done. ACT button out and let fly!

Hope this helps everyone reading this in the future
That's awesome. Thanks for posting.
  Reply With Quote
Old May 26th, 2016, 08:27 PM   #14
rupej
Member
United States

rupej is offline
 
Join Date: Sep 2014
Location: NC
Posts: 938
Interesting- does the VFD actually prevent the drive from starting when the fan run-hours reach a certain limit? Or does it just alarm?
  Reply With Quote
Old June 16th, 2016, 12:00 PM   #15
ranjankamath
Member
India

ranjankamath is offline
 
Join Date: Oct 2010
Location: Mysore
Posts: 1
Thanks for your Post,can you please share ACS 800 Manual containing Parameter Description for Group 145
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
ABB ACS800 & Ethernet Elcan LIVE PLC Questions And Answers 5 May 20th, 2013 11:06 AM
ABB ACS800 Drive Rob S. LIVE PLC Questions And Answers 8 March 19th, 2013 06:00 PM
ABB RETA-01 to ACS800 firmware compatibility Purrdie LIVE PLC Questions And Answers 3 October 24th, 2011 11:02 PM
ABB ACS800 LC firmware TOKG1Tech LIVE PLC Questions And Answers 3 June 14th, 2011 09:13 PM
ABB ACS800 A1>min Fault (8110) thebuzz LIVE PLC Questions And Answers 9 May 14th, 2011 10:13 AM


All times are GMT -4. The time now is 10:30 AM.


.