Issue with wizard for powerflex 525 in studio 5000

jakeparsons03

Member
Join Date
Jun 2017
Location
Indiana
Posts
78
Hey all,

I am having an issue when I get to the direction test of a powerflex 525. It says there is a communication issue. But I can change all parameters still. When I go to tuning it gives another error.

"There was an unhandled exception....object of type RADrvAPI.StatusFeedbackEventArgs cannot be converted to RADrvAPI.LostControlEventArgs"

Has anyone seen this?

Thanks in advance!
 
Not this specific issue, but I've had problems when the logic is trying to control the drive at the same time as doing a test or autotune.
 
Not this specific issue, but I've had problems when the logic is trying to control the drive at the same time as doing a test or autotune.

I was taught to always change the start control to the keypad and disconnect the Ethernet for Auto tuning.

Right or wrong, it works for me 100% of the time. Just make sure the Ethernet loos parameter isn't set to fault.
 

Similar Topics

It's been a while since I've done a Powerflex w/o a hardwired enable (enabling over Ethernet/IP). So I'm struggling with how you are run the...
Replies
2
Views
1,393
Everything was working fine, but suddenly CPU went into error mode, and the ERR and TER LEDs lit up. Now I can't download or connect with the PLC...
Replies
0
Views
32
I have created a project in TIA Portal v16 Upd6 with S7-1200 (6ES7214-1AG40-0XB0) and WinCC Unified (PC station). The communication between the...
Replies
4
Views
144
Hi folks, in the alarm manager of Rslogix 5000, the tag-based alarm has been created. But when I tried to change the condition, it was found the...
Replies
2
Views
149
I have a German programed ME program. I want to know what tag in the PLC a latched button turns on. However when I open up the tag properties I...
Replies
14
Views
199
Back
Top Bottom