I found the problem, well not exactly me, but I was close enough
the steps are as follow:
1-a file in the CX-Programmer needs to be created with the default settings
2- go online and change IP address to the desired one (this time I used 192.169.1.1) and the subnet mask (255.255.255.0)
3- transfer configurations to PLC
4- go to Tools, and choose the second option (network setup I think, mine is in spanish)
5-a small program opens, right click on your PLC and open
6- click in routing tables in the upper tabs set
7-another window opens, go to unit 250, right click, add SIO
8- transfer the table to the plc via options tab, transfer to PLC
9- return to CX-Programmer, quit online, and configure you PLC comms as attachment 1, and in attachment 2 the IP address set in step 2
10- open the red lion, and check for attachment 3.
in attachment 3 (Crimson software for red lion HMI), I went to comms, network, protocol X (you decide the X), choose omron, Master via FINS
then I selected the PLC (name can be changed) and made these settings
on the left side
Destination Network: 0 (seems like needed to be 0)
Destination Node: 1 (last fragment from PLC IP Address)
Destination unit: 0 (also seems like has to be 0)
on the right side:
Source network 1 (the 1 from attachment 1)
Source node: 2 (Last fragment from HMI IP)
Source unit: 1 (also from attachment 1)
My problem was that on the left side I rote the settings for the right side, and in the routing table, I was using the unit 1 slot, and CP1L-E has built-in ethernet port (and only this built in port) that uses the unit 250.
I hope this post will help someone in the future.