I am doing a little self training and looking for some feedback. I have a plc 5 with a 1771-il module looking into some scaling issues with an input. I am looking at changing the raw min and raw max of the BTW of the input and would like to know that when I accept edits on this change a pop up is displayed "do you want to download the configuration to the module". If I download the change will this stop the process?
 
Welcome to the Forum!

You do not have to edit (and you definitely should not) any Block Transfers, Data Table and/or logic in order to adjust any 1771 analog signal scaling.

Use the RSLogix 5 I/O Configuration applet which will provide you with all the available 'adjustable' settings for the analog module's channels; just type in the value(s) and hit the Enter key.

If the respective module's BTW is being processed every scan the new scaling will be implemented immediately; if the BTW is triggered only at Power-Up time you might need to add an XIC of an unused memory bit in parallel with the Power-Up bit and make it '1' then '0' with the PLC5 in Run mode; you could Delete the instruction upon finishing the tweaking in order to prevent someone else to inadvertently change the configuration.
 

Similar Topics

A question was sent via PM this morning from a new member (Vince9521, from up in Timmins, Ontario) that I'm promoting to the main forum:
Replies
1
Views
1,070
Hey everyone, Trying to bench test the I/O on a program that I converted from a PLC-5 processor to a ControlLogix processor but still using the...
Replies
21
Views
6,492
Hi, We have a customer using PLC-5 system with RIO. From what they complain is the slow speed of the PLC DI (normal), thus they wanted to get...
Replies
17
Views
10,436
These two RTD's are wired to channels 1 and 2 on a 1771-IR in a remote rack, communicating to a PLC-5/40 through an ASB. I believe that the RTD's...
Replies
7
Views
1,950
Hello, I am in the process of migrating a PLC-5 system over to ControlLogix and could not find any equivalent modules to convert the 1771-ALX...
Replies
2
Views
1,479
Back
Top Bottom