SLC 5/03 to NET IP

kbradray

Member
Join Date
Jan 2006
Location
Columbia
Posts
175
I am currently trying to install a Net/IP (1761-Net-ENI) module on a SLC 5/03 (5/03 CPU-8K Mem. OS302 Ser. C Fr. 10) I have installed several of these on ML1500s with no issues, but I can’t get this one to communicate with the processor via DF-1 RS 232. I can communicate via the DF-1 port on the processor to my laptop.



I have used the ENI utility to configure the module.

I have verified that both baud rates are the same 19200

I have the correct cable from SLC to Module (supplied by the AB vendor)

With the ML 1500s I am using the cable for the power source to the module, but when I plug in the cable to the 5/05 I get no power to the module.

While my laptop is connected the RS232 light on the processor is blinking, but as soon as I disconnect and hook up the configured Net-ENI module it goes out.



Can someone tell me what I am missing?
 
For that setup you'll need to supply the ENI with external 24VDC and change the power select switch to external instead of cable. Is it a 5/03 or 5/05? You mentioned both.
 

Similar Topics

Hello all! I have some machines that run an SLC 5/03 and occasionally a fault is generated. Recent Example: A power supply wasn't screwed in...
Replies
3
Views
421
Customer has a circa 2004 SLC-500 PLC. Fieldbus is a 1747-SDN DeviceNet scanner. Customer has SLC-500 file (.rss) with no comments. Has no *.dnt...
Replies
7
Views
553
Hello, I've got a project where I need to get information from two ABB ACS880 VFDs onto the plant operator's screen (or alternatively, onto...
Replies
23
Views
2,595
Machine has existing DN devices that are connected to SLC 5/04. All communication is working fine now. Supplier wants to remove some DN devices...
Replies
6
Views
841
I'm having a strange issue where the operator can input a desired speed in 0-110%, and the scaling will correctly translate that in Hertz to the...
Replies
6
Views
2,285
Back
Top Bottom