Point I/O Basics

Narlin

Lifetime Supporting Member
Join Date
Mar 2010
Location
phoenix
Posts
320
[FONT=&quot]Want to set up some point i/o and I haven’t used it before. When searching this forum there is a lot of info but so far not exactly what is needed. Hopefully, I can get some of the basics answered here. [/FONT]​
[FONT=&quot]1. [/FONT][FONT=&quot]My remote location is 200’ from the 1769-L30ER PLC, before any up/down wire routes. If it happens that the cable exceeds 300’, will a powered unmanaged switch placed halfway along the route amplify the signal adequately?[/FONT]​
[FONT=&quot]2. [/FONT][FONT=&quot]If the PLC is connected to an internet accessible router (if, if, if), is it needed to use a managed switch? If so, what does that do that is so wonderful?[/FONT]​
[FONT=&quot]3. [/FONT][FONT=&quot]I figured out how to configure the 1734-AENT/A (Ethernet point communicator) to Logix 5000 in the Controller Organizer (tree view), and how to add point I/O modules. Is there a requirement for 1 IP address for each Point I/O Chassis? The L30ER is limited to 16 ethernet nodes. Is this why there is more than one node? [/FONT]​
[FONT=&quot]The remote part of the tree is as follows:[/FONT]​
[FONT=&quot]-Ethernet[/FONT]​
[FONT=&quot] ---1769-L30ER Generic1[/FONT]​
[FONT=&quot]- 1734-AENT/A RCOM01[/FONT]​
[FONT=&quot] - PointIO 10 Slot Chassis[/FONT]​
[FONT=&quot] [0] 1734-AENT/A RCOM01[/FONT]​
[FONT=&quot] [1] 1734-IE2C/C RI01[/FONT]​
[FONT=&quot] [2] 1734-OB4/C RO02[/FONT]​
[FONT=&quot] [/FONT]​
[FONT=&quot]4. [/FONT][FONT=&quot]My CMore OIT will be communicating over Ethernet too. Is it a node?[/FONT]​
[FONT=&quot]5. [/FONT][FONT=&quot]If a virtual 10 Slot Chassis for 1734-AENT is created, but then only 2 slots are used, what is wasted? Is it just controller memory? If so, there seems to be plenty of that.[/FONT]​
[FONT=&quot]6. [/FONT][FONT=&quot]How do I address the remote data from Logix 5000? When I alias local I/O, I use [LOCAL:1:O.DATA.0] for example for the 1st bit of an output card in local slot 1. For the remote I/O, I have named the 1734-AENT = “RCOM01”. I have the following memory locations.[/FONT]​
[FONT=&quot]+RCOM01:I[/FONT]​
[FONT=&quot]+RCOM01:O[/FONT]​
[FONT=&quot]+RCOM01:1:C[/FONT]​
[FONT=&quot]+RCOM01:1:I[/FONT]​
[FONT=&quot]+RCOM01: 2:C[/FONT]​
[FONT=&quot]+RCOM01:2:O[/FONT]​
[FONT=&quot] [/FONT]​
[FONT=&quot]To alias (and later address) an input bit from the IE2C in slot 1, I expand +RCOM01:1:I, followed by expanding +RCOM01:1:I.Ch0Data[/FONT]​
[FONT=&quot]It looks like this:[/FONT]​
[FONT=&quot]-RCOM01:1:I[/FONT]​
[FONT=&quot] +RCOM01:1:I.Fault[/FONT]​
[FONT=&quot] -RCOM: 1:I.Ch0Data 0[/FONT]​
[FONT=&quot] -RCOM: 1:I.Ch0Data 1[/FONT]​
[FONT=&quot] -RCOM: 1:I.Ch0Data 2[/FONT]​
[FONT=&quot] -RCOM: 1:I.Ch0Data 3[/FONT]​
[FONT=&quot] -RCOM: 1:I.Ch0Data 4[/FONT]​
[FONT=&quot] -RCOM: 1:I.Ch0Data 5[/FONT]​
[FONT=&quot] -RCOM: 1:I.Ch0Data 6[/FONT]​
[FONT=&quot] -RCOM: 1:I.Ch0Data 7[/FONT]​
[FONT=&quot] -RCOM: 1:I.Ch0Data 8[/FONT]​
[FONT=&quot] -RCOM: 1:I.Ch0Data 9[/FONT]​
[FONT=&quot] -RCOM: 1:I.Ch0Data 10[/FONT]​
[FONT=&quot] -RCOM: 1:I.Ch0Data 11[/FONT]​
[FONT=&quot] -RCOM: 1:I.Ch0Data 12[/FONT]​
[FONT=&quot] -RCOM: 1:I.Ch0Data 13[/FONT]​
[FONT=&quot] -RCOM: 1:I.Ch0Data 14[/FONT]​
[FONT=&quot] -RCOM: 1:I.Ch0Data 15[/FONT]​
[FONT=&quot] [/FONT]​
[FONT=&quot]Is this where the data will be? Why are there 16 bits? The card can only handle 2 points – my understanding is that’s 2 bits worth (pun intended). Do i only use Data 0 and Data 1?[/FONT]​
[FONT=&quot] [/FONT]​
[FONT=&quot]Similarly but worse, with the OB4, I only see 8 bits. The output card only handles 4 points.[/FONT]​
[FONT=&quot] [/FONT]​
[FONT=&quot]Manuals: RTFM. I have this publication. [/FONT][FONT=&quot]1734-UM011D-EN-P POINT I/O EtherNet/IP Adapter Module User Manual. It talks about all the different cards, but from my basics, i haven’t been able to get many answers from the manual.[/FONT]
[FONT=&quot] [/FONT]​
[FONT=&quot]This is too much for now. I will stop and hopefully get some answers.[/FONT]​
 
Get the 1734-SG001 Selection Guide for the POINT I/O family. It addresses a lot of the higher-level questions about how POINT I/O is selected and installed.

Your friendly neighborhood A-B distributor may be able to help you get introduced to these technologies too.

But I'll take a shot at some of your questions.

1. Yes, you'll need a repeater or switch if your Ethernet cable is more than 100 meters long. Fiber optics is really great for long distances, too.

2. Managed switches are great for telling you when you're getting bad signal on the device, and they're great for constraining multicast traffic. Multicast isn't required in a single-controller network so the need for managed switches is less than it used to be. I still like to get them when I can, because nothing's more frustrating than troubleshooting a network that has no diagnostic features.

3. RA simplified the "CIP connections and TCP connections" when they rolled out the new CompactLogix 5370 family. Instead they just say "node", and provide enough CIP capacity to handle anything you can connect.

4. A 1734-AENT is a Node, and a C-More is a Node, and your laptop PC is a Node.

5. The "Chassis Size" set in the 1734-AENT and the Chassis Size value in RSLogix 5000 have to match. If you create a 10-slot "Chassis" but have 2 modules installed the connection won't run.

Oh, and when you're setting up, use the 1734-AENT/B. It's not easy to switch between Series letters once it's already configured, and all new stock has been Series B for a couple of years.

6. For the 1734-IE2C, Analog data is in 16-bit Words, so you won't be addressing the individual bits.

For the 1734-IE2C module, the two analog channels will have their input data in RCOM:1:I.Ch0Data and RCOM:1:I.Ch1Data.

The CompactLogix uses a SINT as the data container for all the 2 and 4 and 8 bit discrete modules. The unused bits are just unused.
 
[FONT=&quot]1. [/FONT][FONT=&quot]My remote location is 200’ from the 1769-L30ER PLC, before any up/down wire routes. If it happens that the cable exceeds 300’, will a powered unmanaged switch placed halfway along the route amplify the signal adequately?[/FONT]​
I would never use a switch to extend distance. You now have to get power to a third location between your cabinets and now your switch is not located with any other equipment. If you need to go more than 100m use fiber media. It's the right thing to do.
[FONT=&quot]2. [/FONT][FONT=&quot]If the PLC is connected to an internet accessible router (if, if, if), is it needed to use a managed switch? If so, what does that do that is so wonderful?[/FONT]​
I wouldn't bother with an unmanaged switches, ever. The big three reasons: no security, no network segmentation, no diagnostics.
 
My RSLogix 5000 is V20.03.00(CPR 9 SR 5). When i add the 1734-AENT, only series A is available inthe drop down. how do you get B?
 
Last edited:
3. RA simplified the "CIP connections and TCP connections" when they rolled out the new CompactLogix 5370 family. Instead they just say "node", and provide enough CIP capacity to handle anything you can connect.

4. A 1734-AENT is a Node, and a C-More is a Node, and your laptop PC is a Node.

I agree with most that you have put down except the evaluation of Nodes.

1734-AENT is a Node

C-More Might be a Node (Only if it is in the I/O configuration section. I know I never put Panelviews there so they would NOT be considered a Node)

Laptop is NOT a Node

Check out 474754 on the knowledgebase

I have attached it for those without access
 
The Cmore OIT does not have to be listed in the tree. It works very similarly to a PanelView (but in my opinion - easier). I never really thought my laptop was node. It would be interesting to load up the L30ER or a lesser model and see if when all nodes were full you could still connect with the laptop.
 
There is 1 glaring error in the original post. I mistakenly named an analog module IE2C, whenever I intended to have put in a digital module. When the correct digital module was put into the tree, everything made sense.
 
The Cmore OIT does not have to be listed in the tree. It works very similarly to a PanelView (but in my opinion - easier). I never really thought my laptop was node. It would be interesting to load up the L30ER or a lesser model and see if when all nodes were full you could still connect with the laptop.

I have already tested the "Node" theory. You will get an error (once you compile) if you add too many nodes.
 

Similar Topics

Hi, I have some problem with View Point which I'm using to manual control of conveyors. On begin when in network was only PLC and HMI View Point...
Replies
0
Views
69
I have a bunch of tags in Historian/VantagePoint that off by one decimal point. I looked into the HMI displaying the same number, and the HMI is...
Replies
2
Views
113
Good morning, I have a Emerson/GE PLC with Cimplicity SCADA. I need to export data of a specific point/object to a CSV file and load the CSV file...
Replies
7
Views
274
Dear We are working in AB Studio 5000 and the drive is a PowerFlex 755T. For this project I need to control a conveyor to a certain set point...
Replies
2
Views
131
Hello colleagues Anybody knows, what could be the best or a better option to bring with you when you are in service at factory to connect via...
Replies
1
Views
259
Back
Top Bottom