So I have a project with a couple of thermocouple cards on an Allen Bradley L33ER rack. The instruments aren't due in for a little while, and I want to test out the signal high/low. I have an analog signal generator for mA and 0-10, but thermocouples send in a mV signal, correct?
Any good way to bench test these inputs? Is it as simple as making a voltage divider with a potentiometer reducing the voltage to the mV range?
Better to use a specific thermocouple simulator since the signal at the analog input is the difference between the mV generated in the hot junction minus the mV of the cold junction.
It could also be done with a simple mV generator if you apply the difference of mV explained above.
If you use the correct TC extension wire, and you have a millivolt output meter.
Run copper wire from meter and twist together with the TC extension wire. Make sure you remember that Type K wire colors are Red=Neg and Black = positive.
Now get a glass of ice water (lots of ice) and insert the junctions you twisted together in the glass of ice. Now you have created a "cold Junction" at 32 degrees. The water will stay at very near to 32 deg. till the ice melts.
You can use the millivolt reference table from here to test the PLC module. And now you do not have to correct for the different temperature errors at the copper to Type K wire junction.
https://www.thermocoupleinfo.com/thermocouple-reference-tables.htm
If they are 4 channel thermocouple cards, not 8, you can:
Make a copy of the project.
Change the IO Config to 4 channel input analog input cards
Test the program using mA or voltage signals.
Any changes needed make to the original also, ,or change the IO back to thermocouple.
If 8 channel inputs and you have extra slots on the rack you could put 2 analog inputs for a thermocouple input & change some addresses.
You don't need to create a 0°C cold junction or use TC extension cable.
Measure the ambient temperature near the module, then look in the TC table the mV that correspond to the ambient temperature, then look the mV for the temperature you want to simulate and apply the difference between the two voltages in the module terminals.
I am working on setting up a Prosoft Datalogger model PLX51-DLplus-232. This unit will be collecting data from a SLC 5/05 on the DB9 port set to...
97
Hi all, I have a AC current transducer that I want to bench test to ensure I am getting a 4-20mA output. I am using a AE001 unit. It is very...
116
Hi Guys, Can ControlLogix with Modsim32 for Modbus Server Testing? I have ControlLogix via Anybus Modbus TCP and I need to Test the...
308
Hello all, looking for ideas on getting some basic training done, I need to practice on maintenance timers and bypass switches (with a Factory...
1,313
I have a project in FTV ME (Studio v13) that I'm trying to apply security to a few buttons/setpoints. I have 4 users: Anonymous Logon, DEFAULT...
784