Hello everyone,
I am relatively new in PLCs. I have 2 PLC trainers (one having Micrologix 1200 series A and the other Micrologix 1200 series C). I have a RS 232 cable for each trainer to its corresponding PC.

Problem: I have to network these two trainers using a single workstation. The softwares I have are RSLogix 500 and RSLinx. When I open RSWho, I see AB_DF1-1, DH485 as network name. Its properties: AB_DF1-1 as device name and device SLC-CH0\Micro\PanelView with full duplex protocol.

What should I do or buy to network these two trainers, I am looking for the cost-effective solution. I have visited the Allen-Bradley website and am lost in the manuals section. Again as I told before, I am new to this field.

Regards,
Taknevs
(grad student)
 
RS-232 is really a one to one communications scheme, and does not usually cope well with multi-drop systems. You need to use an Allen Bradley AIC+ unit to multidrop the PLCs. This is essentially an RS-485 network which can cope with multi-drop.
 
Hi again,
Thanks for the help. So what I need is individual AIC units for the PLCs and PC and a hub for the DH-485 network, correct?

regards,
taknevs
 
Close, but not quite. The AIC has one RS-485 port, and two RS 232 ports. So, you can use two AIC's. One AIC will use both RS232 ports, one of which will connect to the ML-1200 and the other to the PC. One AIC will connect to the ML-1200. The 485 terminals on each AIC will be connected to each other.

Now that you have some better info, perhaps you can locate the manual at ab.com by searching on AIC+
 

Similar Topics

Good morning all, We have a micrologix 1200 that we are using to control our plant water operation. We are having an issue with being able to...
Replies
5
Views
2,329
We have several dozen PLC5's, some with ethernet cpu's and some with DH+. We have upgraded as convenient the DH+ to ethernet with bridges so they...
Replies
7
Views
3,096
I am in need of having a machine (sewage lift station) send a message when it is in alarm status. After talking to my AB rep I have desided on...
Replies
3
Views
7,567
Hi Folks...Over the past couple of weeks I've aquired a couple of used PLCs. One is a micrologix 1000 1761-L16AWA and the other is a SLC500...
Replies
2
Views
3,027
I have a client who periodically experiences network communication issues. Sometimes when I VPN into the site, their SCADA systems will flash comm...
Replies
2
Views
75
Back
Top Bottom