Point IO burned up.

We have a system with several Point IO panels. Today had one that burned from the Field Potential Distributor Module. The 120vac output card beside the FPD looked like it had a lot of burn marks but since it is the next card to the right its hard to tell where the problem originated from. Most of the damage was around the terminal block where the FPD receives 120vac power. The other Point IO panels get 120vac from the same source.

Reading about the FPD and its function i think i can rule out the DC side being part of the problem. The 120v output supplies three solenoid valves to control liquid. The valves all test ok using a meter.

There is no suppression devices on these valves. They are not even fused. What do you guys think about adding simple fused terminal blocks to these? Has anyone had one of these fail like this? Any thoughts on the cause? Thanks
  Reply With Quote
Old May 6th, 2021, 07:08 PM   #2
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 16,963
I've certainly seen 120V AC circuits burn up when they get contaminated, overloaded, shorted to ground, etc.

The fact that it was in the context of a POINT I/O assembly and a 1734-FPD Field Potential Distributor just suggests to me that the isolation did its job and kept the damage to the associated circuits, not the network, the adapter, or the backplane.

If everything's charred there's not much chance of finding contamination, or loose screw terminations, that could be the cause.

I agree that it would be prudent to protect the field wiring for those solenoids with a fuse on the "hot" leg where it enters the 1734-FPD, sized to accommodate all of the solenoid loads while protecting the wiring.

What is the wattage of the solenoid coils ?

In general, solid-state AC outputs don't suffer from the same kind of flyback / spike risk and damage as dry relay contacts do. What exactly was the 1734 I/O module ? Was it an "OA" (triac) or an "OX" (relay) ?
  Reply With Quote
Old May 6th, 2021, 08:25 PM   #3
dftmaint
Member
United States

dftmaint is offline
 
Join Date: Nov 2017
Location: TN
Posts: 7
Quote:
Originally Posted by Ken Roach View Post
I've certainly seen 120V AC circuits burn up when they get contaminated, overloaded, shorted to ground, etc.

The fact that it was in the context of a POINT I/O assembly and a 1734-FPD Field Potential Distributor just suggests to me that the isolation did its job and kept the damage to the associated circuits, not the network, the adapter, or the backplane.

If everything's charred there's not much chance of finding contamination, or loose screw terminations, that could be the cause.

I agree that it would be prudent to protect the field wiring for those solenoids with a fuse on the "hot" leg where it enters the 1734-FPD, sized to accommodate all of the solenoid loads while protecting the wiring.

What is the wattage of the solenoid coils ?

In general, solid-state AC outputs don't suffer from the same kind of flyback / spike risk and damage as dry relay contacts do. What exactly was the 1734 I/O module ? Was it an "OA" (triac) or an "OX" (relay) ?
It was charred real bad. I couldn't see the wattage but each were reading around 180 ohms which would be pushing the rated .75 amps each output is rated. It was an OA4.

Last edited by dftmaint; May 6th, 2021 at 08:32 PM.
  Reply With Quote
Old May 6th, 2021, 08:40 PM   #4
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 16,963
Thanks for those details !

You are correct, of course, that the 1734-OA4 is rated for 750 mA per output, and 2A total per module.

Sanity check: V/R = I, so 120/180 = 0.660 Amperes.

While POINT isn't as rugged as ancient 1771 stuff, the ratings are still fairly conservative and the max current is for continuous operation at 113F ambient.

Maybe there was a floating or loose ground and you ended up rattling those solenoids on and off and burned the module up with surge current.

If you wanted to be even more conservative, put in another 1734-OA4 and move one of the solenoids to it.

But in general there's nothing mysterious or complicated about an OA4 triac output. Fuse the output to protect the wiring, and check all the wiring all the way through for loose terminals on the neutral side.
  Reply With Quote
Old May 6th, 2021, 09:22 PM   #5
dftmaint
Member
United States

dftmaint is offline
 
Join Date: Nov 2017
Location: TN
Posts: 7
The plc is a compactlogix and we don't have Rslogix 5000 to make changes. I have some, but not a lot of RS5000 experience. Really just the few programs i did in tech school and a trainer i completed. Would i would need to change an address in the program if i added another terminal block and module to the point IO? Most of our stuff is slc 500, micrologix, or automation direct. May just add interposing relays to get isolation. Thank you for all the help.
  Reply With Quote
Old May 6th, 2021, 09:52 PM   #6
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 16,963
Yes, you would need to change the I/O configuration in RSLogix 5000, and maybe make a change to the POINT rack size through its web browser too.

Generally I/O modules don't just burn up spontaneously on overload if they've been specified correctly, especially if you have similar circuits that don't overload.

Inspect all the wiring to those valves carefully. A loose neutral could certainly cause a malfunction like what you described, typically along with "valve chatter".
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
1734 ADN Point IO status bornwild LIVE PLC Questions And Answers 6 October 17th, 2018 07:41 AM
Point IO Analog scaling kjacoby LIVE PLC Questions And Answers 12 May 24th, 2017 01:06 PM
Point IO Analog In 1734-IE2C Not reading harryting LIVE PLC Questions And Answers 10 June 5th, 2015 10:12 AM
Point IO Cable Length Ray S LIVE PLC Questions And Answers 4 January 7th, 2013 12:18 PM
Point IO 4 Point AC-DC Relay Output configuration JNS LIVE PLC Questions And Answers 1 April 27th, 2011 12:51 PM


All times are GMT -4. The time now is 10:24 PM.


.