There is an instruction called a drum in AD software. Here it is in DoMore; I would think Click would be similar, but who knows. All it does is trade @parky's several [if step=N and (step N complete) then step = {step + 10}] sequence transition rungs for a behemoth of an instruction.
It does save a few rungs for setting outputs. It does not have the pass-fail logic, and I am assuming the input raw WX0 16-bit integer is pressure in dPSI, so it will not be any shorter than @parky's in the end. There is a bug when the DoMore simulator starts, in that for some reason C3 seems to start with an initial value of 1, which jogs the Drum to Step 2. I have not been able to figure out why, so if anyone can give me a hint; I am loathe to think it's a bug in the simulator. But once the drum either completes a cycle or has been reset, then it runs as expected. Untitled.png
__________________
_ Brian T. Carcich i) Take care of the bits, and the bytes will take care of themselves. ii) There is no software problem that cannot be solved with another layer of indirection. iii) Measurement is hard. iv) I solemnly swear that I am up to no good ![]() v) I probably have the highest ratio of forum posts to actual applications in the field (∞). vi) Hakuna matata. |
![]() |
![]() |
#62 |
Member
|
Yes the click does have Drum.
|
![]() |
![]() |
#63 |
Lifetime Supporting Member
|
__________________
_ Brian T. Carcich i) Take care of the bits, and the bytes will take care of themselves. ii) There is no software problem that cannot be solved with another layer of indirection. iii) Measurement is hard. iv) I solemnly swear that I am up to no good ![]() v) I probably have the highest ratio of forum posts to actual applications in the field (∞). vi) Hakuna matata. |
![]() |
![]() |
#64 |
Member
|
Just incase you are struggling, below is a pic of how to setup the analogs
On the left navigation pane select the tab for Function then click the I/O configuration & select Built in I/O In the popup select input and at the bottom are the analog inputs, select 4-20ma for both channels, change the scaled range to what ever your transducer is, you do not have to change the pre-populated registers it defaults to DF1 & DF2 (they can be changed but why bother) these are floating point (real) registers, click on the output & do the same for the analog outputs I suggest the scaled range be 0-100.0 (for %) this is standard as if this was a PID fed it makes sense all it means is you are driving the I/P (4-20 ma) at 0-100% so when you send the flow setpoint to the I/P (motor). just so you know. X are inputs Y are outputs C are internal Bits to use in program T are timers CT are counters DS are 16 bit registers (integers) DD are 32 bit registers (long integers or double integers) DH are 16bit hex registers DF are floating point (32 bit) registers SD are system data registers (used for information i.e coms status etc. SC are system control bits, these contain things like always true bit one scan on start up, clock bits like 10ms clock, 10ms clock, 1 sec clock etc. SC & SD have symbols already so tell you what they are. If you click on the address picker from the top menu (press home button first) it brings up a popup where you can edit the symbols (descriptions)of what all the I/O, registers etc. you are using are. |
![]() |
![]() |
#65 |
Member
![]() ![]() Join Date: Jan 2023
Location: bangalore
Posts: 1
|
Most PLCs can be programmed using a standard computer and PLC programming software. The International Electrical Code's IEC 61131-3 standard defines five languages for PLC programming.
|
![]() |
![]() |
#66 |
Lifetime Supporting Member
|
I was able to workaround my DoMore bug by adding a Run input (X2) that resets the drum whenever it is off, so even though C3 comes on for some reason when the simulator starts, it is reset in the drum.
__________________
_ Brian T. Carcich i) Take care of the bits, and the bytes will take care of themselves. ii) There is no software problem that cannot be solved with another layer of indirection. iii) Measurement is hard. iv) I solemnly swear that I am up to no good ![]() v) I probably have the highest ratio of forum posts to actual applications in the field (∞). vi) Hakuna matata. |
![]() |
![]() |
#67 |
Lifetime Supporting Member
|
Heh. Sequence logic can be placed on one rung, at least in DoMore:
Untitled.png
__________________
_ Brian T. Carcich i) Take care of the bits, and the bytes will take care of themselves. ii) There is no software problem that cannot be solved with another layer of indirection. iii) Measurement is hard. iv) I solemnly swear that I am up to no good ![]() v) I probably have the highest ratio of forum posts to actual applications in the field (∞). vi) Hakuna matata. |
![]() |
![]() |
#68 |
Lifetime Supporting Member
|
Typo: (2) is Pumping, not Holding
__________________
_ Brian T. Carcich i) Take care of the bits, and the bytes will take care of themselves. ii) There is no software problem that cannot be solved with another layer of indirection. iii) Measurement is hard. iv) I solemnly swear that I am up to no good ![]() v) I probably have the highest ratio of forum posts to actual applications in the field (∞). vi) Hakuna matata. |
![]() |
![]() |
#69 |
Member
|
Yeah, used a drum sequencer on another platform did not like it limited steps, on that one could not step back & TBH it took more processor time than rolling your own, but that is probably because of the different functions.
The only other one I came across was in Siemens S5, it was a sort of drum sequencer it was not built in but a add on function, I managed to open it up & look at the MC5 code, again it was quite large the engineers at that site hated it as they did not understand it, found it difficult to follow Mitsubishi have SFC again step transition is hard to follow if you did not program it, most engineers I know hated it. |
![]() |
![]() |
#70 |
Member
![]() ![]() Join Date: Jan 2023
Location: Louisville, Ky
Posts: 72
|
@drbitboy @parky Hello I am back from the weekend. Time to get to work. I will read all the things you guys posted. It seems like you guys really want to help, I really appreciate it. I will do some more learning from what you recommend and also the codes you posted. I have skimmed through them, and it all makes sense to me so hopefully I can get something out of this week. I am planning to learn more about the electrical side of the PLC. If I don't know how everything connects then how will I know what PLC to get, so that's why I will focus on that. Also, I will give you my parts list I made already if you two want to skim over it.
NCP2-20-3120N ( pressure transducer, current to pneumatic transducer)- https://www.automationdirect.com/adc.../ncp1-20-3120n SPT25-20-2000A (pressure transmitter)- https://www.automationdirect.com/adc...spt25-20-2000a EA9-T6CL-R (hmi touchscreen)-https://www.automationdirect.com/adc/shopping/catalog/hmi_(human_machine_interface)/c-more_touch_panels_ea9_series/c-more_ea9_series_touch_panels/ea9-t6cl-r PARKER GRESEN Pressure Relief Valve: 0 to 2000 psi (mechanical relief valve)-https://www.grainger.com/product/38D924?gucid=N:N:PS:Paid:MS:CSM-2295:TVRYAD:20501231&gclid=9335421c701c1e763b3f21d c7e0b7dd5&gclsrc=3p.ds&gclid=9335421c701c1e763b3f2 1dc7e0b7dd5&gclsrc=3p.ds&msclkid=9335421c701c1e763 b3f21dc7e0b7dd5 Solenoid Valve: 1/4 in Pipe Size - Valves, 120V AC, 0 psi Min. Op Pressure Differential- https://www.grainger.com/product/RED...-in-Pipe-6WTT0 Click C0-12DRE-1-D- https://www.automationdirect.com/adc...s/c0-12dre-1-d Click Power Supply C0-00AC- https://www.automationdirect.com/adc...pplies/c0-00ac Serial to RJ-12 cable for hmi- https://www.automationdirect.com/adc...cables/ea-2cbl Last edited by Aljubovic; January 16th, 2023 at 07:22 AM. |
![]() |
![]() |
#71 | |
Lifetime Supporting Member
|
Quote:
I agree: your step coding is easier to follow and debug. I did it because the drum satisfies my "code golf" bent. It will do less so without hard-coded pressure levels and pump speeds. This is a simple sequence, so drum might work for OP; it seemed worth presenting all the options.
__________________
_ Brian T. Carcich i) Take care of the bits, and the bytes will take care of themselves. ii) There is no software problem that cannot be solved with another layer of indirection. iii) Measurement is hard. iv) I solemnly swear that I am up to no good ![]() v) I probably have the highest ratio of forum posts to actual applications in the field (∞). vi) Hakuna matata. |
|
![]() |
![]() |
#72 |
Member
![]() ![]() Join Date: Jan 2023
Location: Louisville, Ky
Posts: 72
|
I will try to recreate Parky's type of code into click programming software. I will see how it goes and post my results here
|
![]() |
![]() |
#73 |
Member
![]() ![]() Join Date: Jan 2023
Location: Louisville, Ky
Posts: 72
|
Hello. I figured out how our pump system works when doing manual testing. Here is the basic diagram I made.
https://imgur.com/a/wuwJs35 There is a compressor that has a constant 140psi pressure of pneumatic air that is fed into the pump system. The first pressure gauge also has a manual knob on it to let the compressed air into the pump. As the pump starts building pressure it builds pressure in the water at the outlet of the pump. I think that the current to pneumatic transducer will work, but couldn't I just use a solenoid valve or some sort of electronic control valve instead of the transducer? Not sure if that would be a great idea because the transducer can accurately give out a certain amount of pressure while the valve can be open halfway and we don't know how much pressure is being let it. Last edited by Aljubovic; January 16th, 2023 at 09:42 AM. |
![]() |
![]() |
#74 | ||
Lifetime Supporting Member
|
Quote:
Good idea. That will allow you to partition the code for each section and make it easier to understand. Btw, you never answered this: Quote:
It sounds like the I-to-P is the same as the manual knob i.e. a pressure regulator, and the air-driven pump will stop moving liquid into the test part when it stalls i.e. when the regulated air pressure to the air-driven pump is the water pressure divided by the pump's pressure ratio (minus some frictional ε). If that is the case, and assuming the pressure rise is slow enough, I suggest a simple proportional control algorithm:
__________________
_ Brian T. Carcich i) Take care of the bits, and the bytes will take care of themselves. ii) There is no software problem that cannot be solved with another layer of indirection. iii) Measurement is hard. iv) I solemnly swear that I am up to no good ![]() v) I probably have the highest ratio of forum posts to actual applications in the field (∞). vi) Hakuna matata. Last edited by drbitboy; January 16th, 2023 at 10:24 AM. |
||
![]() |
![]() |
#75 |
Lifetime Supporting Member
|
P.S. those values, the 10PSI (pad and AO channel Scaled Range upper limit), when to start tailing off the AO (PHMI ± some ΔP, to be added with the pad to calculate PHMIplus10), will depend on the system, and could even come from the HMI.
E.g. at lower test pressures or test parts with smaller volumes, the rise may be too fast and require a larger pad and/or an earlier start of the tail, and vice versa for higher pressures. As time and experience is gathered, it might be possible to derive an algorithm based on the target test conditions.
__________________
_ Brian T. Carcich i) Take care of the bits, and the bytes will take care of themselves. ii) There is no software problem that cannot be solved with another layer of indirection. iii) Measurement is hard. iv) I solemnly swear that I am up to no good ![]() v) I probably have the highest ratio of forum posts to actual applications in the field (∞). vi) Hakuna matata. Last edited by drbitboy; January 16th, 2023 at 10:27 AM. |
![]() |
![]() |
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
Thread Tools | |
Display Modes | |
|
|
![]() |
||||
Thread | Thread Starter | Forum | Replies | Last Post |
plc program omron errors | ngoclan | LIVE PLC Questions And Answers | 0 | October 14th, 2014 06:03 AM |
Plc suggestion | aec | LIVE PLC Questions And Answers | 36 | January 2nd, 2012 01:56 AM |
Mitsubishi GX Developer - uploading/downloading program from PLC | mkac | LIVE PLC Questions And Answers | 7 | June 17th, 2010 05:31 AM |
SLC 500 Ethernet Setup | JSPLC | LIVE PLC Questions And Answers | 3 | June 1st, 2010 05:15 PM |
Simulator, Simulation, Shadow Code | Terry Woods | LIVE PLC Questions And Answers | 1 | January 2nd, 2005 02:40 PM |