1752-L72S ControlLogix Controller.

I've been asked to store data on recipes. It will be a simple cumulative weight for each recipe which may change daily. I imagine setting this part up will be simple enough but they are wanting reliable data to be used on daily, weekly and monthly reports. We have an SQL system that I don't have access to so I'd prefer to do it all within the program.

We do weekly (or more) shutdowns of the equipment including powering down the controllogix controller. Many have UPS, some dont. *shrug*

If I create a tag to track the weights and we lose power to the controller there is no chance of recovering/saving the data correct?
 
This should be very easy.

The 1756-L7x series has a capacitor and a flash NVRAM system for the user program. When you shut down power, the controller runs for a few seconds to store the current program and the current value of all the tags in the controller.

Once it shuts down, the NVRAM storage keeps the data indefinitely. The only thing that is affected by extended power-down is the real-time clock.

There are also some application notes for writing tags to the SD storage card in the controller, which can give you some additional survivability of the data in the event of a controller hardware failure.
 

Similar Topics

Hello, We have a customer with a 1756-L72 ControlLogix PLC. They have recently got a T01:C62 Fault Code. I am trying to figure out how to...
Replies
6
Views
1,006
I would like a sanity check on an application i am working on. I have a proximity switch counting pulses with a Mark/space ratio of 1:1 on a...
Replies
2
Views
1,869
Hey Members, I hope all of you are doing well , I am using a 1756-l72 redundancy system, communicating RIO on DLR network. When both my PLC are...
Replies
2
Views
2,398
Hello all.... I am not asking you to fix my issue just a little guidance is all i am asking. I just started with a new company and I am working...
Replies
4
Views
2,594
just need to convince myself what I am doing is OK. Have a project where I am splitting up the process into two 1756-L72 CPUs on an A10 rack. I...
Replies
4
Views
3,434
Back
Top Bottom