I have a client who has installed a control system which was designed offshore (ASIA), and uses a power system common to the Asian market.

The DC power supplies for this control system are all ungrounded, inputs are sourcing and outputs are sinking.

His concern is that a wire 'could get grounded and cause an input, or fire an output', and wonders if a DC Ground Protection device might help, if the DC Common of all the power supplies were tied to ground.

The control power is 24VDC, which is below the NFPA 70 limit of 60VDC for touch-safe.

For myself, I cannot recall any regulatory guidance on the topic of grounding 24VDC power supplies, but was curious as to the opinions of others.
 

Similar Topics

Good day Forum Members I got a older Lincoln welder and hoping to make it work at our shop. Welder in question is the Lincoln Power Wave 455M...
Replies
4
Views
191
I am trying motor startup with pf525 drive by using wizard start over ethernet communication but during direction test it's showing control error...
Replies
3
Views
176
Long ago, it was often a customer spec to always use a transformer for isolation of the control circuit from the rest of the equipment. For 24vdc...
Replies
5
Views
671
Hello Members We have a controllogix redundancy setup and need to display the status of redundancy in panelview. I have found in the manual the...
Replies
8
Views
1,243
Hello, I am currently working on a project that requires the equipment to vary DC power output during cycle. I need to vary from ~30VDC to...
Replies
6
Views
717
Back
Top Bottom