connecting a micrologix 1200 to a panelview 1000
I would like to know if it is possible to connect a Panelview 1000 (cat 2711-T10C8) that has DH+ to a micrologix 1200 with or without a AIC + (cat 1761-NET-AIC) Panel builder 32 software.
Last edited by bpreissner; December 12th, 2016 at 02:15 PM. Reason: More information added |
![]() |
![]() |
#2 |
Lifetime Supporting Member + Moderator
|
It's technically possible to put a 1770-KF2 or equivalent DH+ to DF1 converter between a DH+ equipped PanelView Standard terminal and a MicroLogix 1200 controller, but it's not economically feasible.
The 1761-NET-AIC is an electrical RS-232 to RS-485 converter. It cannot connect to a DH+ network, which uses a proprietary differential signaling method. You probably noticed an RS-232 port on the PanelView terminal. That's for serial printing or upload/download only; it cannot be used for runtime communications. |
![]() |
![]() |
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
Thread Tools | |
Display Modes | |
|
|
![]() |
||||
Thread | Thread Starter | Forum | Replies | Last Post |
Micrologix 1200 to PanelView1000e | dkucukar | LIVE PLC Questions And Answers | 5 | August 27th, 2015 06:38 PM |
Communication between PanelView Plus 700 and MicroLogix 1200 | W.W. | LIVE PLC Questions And Answers | 0 | December 16th, 2010 04:48 PM |
panelview 300 to micrologix 1200 | wayne012 | LIVE PLC Questions And Answers | 18 | May 6th, 2010 11:39 AM |
micrologix 1200, and 1000 question | darrentpi | LIVE PLC Questions And Answers | 4 | July 24th, 2008 06:42 AM |
MicroLogix 1200 Channel 0 Lockup | jgreenewv | LIVE PLC Questions And Answers | 0 | September 2nd, 2004 07:14 PM |