Plc 5

3 pump control

Attached should be the pictures of the front panel and the SLC 5/03. Thanks for the feedback on the Ethernet connection. WOW! Don't need any damage to my computer.
This MCC cabinet has been purchased from another golf course since the old one was washed away and was using 2 motors at 240 volt. We will upgrade to 3 phase 480 volt and add another motor since their motor set up was saved and refurbished resulting in 3 motors and pump system.
Each motor will run a bank of sprinklers for an hour beginning at certain times (beginning at midnight and run sequentially then start over at midnight the next night and so on)
The pressure switches (press sw 1,2,3) will be installed on all three motors on the discharge of the pump to shut down the motor if pressure reaches 130 psi as overpressure protection.
The front panel (pictures) currently has on/off switches for pump 1 and 2 (top row). The bottom row has the Hand/off/Auto switch which I haven't put into the program yet.
The suction side of the pump will come from a pond with a foot valve which may need a priming system to prime the pumps. I will check on that. You will also notice vari-drive controls on the front panel. This drive system will not be used in this system as no manipulated flow control will be required as pumps and motors have been sized to run at full load and maximum pressure. Thank you

Front Panel.jpg SLC 5.JPG
 
The pressure switches (press sw 1,2,3) will be installed on all three motors on the discharge of the pump to shut down the motor if pressure reaches 130 psi as overpressure protection.

So let me see if I'm envisioning the sequence correctly:

  1. Pump is running to a clogged pipe.
  2. Pressure goes >130 PSI, tripping the switch.
  3. Pump stops.
  4. With no motive force behind it, pressure drops to <130 PSI.
  5. Pressure Switch is now OK.

Does the pump restart in AUTO?
If not, when/how does it restart?
How does a human know that there is a problem, since the switch reads "OK"?
 
Great questions. I do not want the motor to restart so I need to review that again. The only equipment in the loop for each pump will be the pressure switch causing shut down. Of course the motor overloads will also shut down the motor, but that will be in the reset system. Manual reset. It would not be a bad idea to put a flag of some sort on the pressure switch to let us know that there was an over pressure, but I would not want the motor to restart until we can determine the cause of the over pressure. The intent here would be simplicity for cost reasons. This is a poor small town 9 hole golf course we th very little money and trying to keep there equipment cost down as we are volunteering no the labor, however we do want to keep the system safe and reliable to keep their future cost down. Thanks again for all of the feedback.
 
A good budget idea is to put a general "alarm" light on the panel for situations that require operator interaction. You could then have the alarm reset when the switch position is changed to OFF. The operator can then switch back to AUTO to attempt to run again.

An even better approach would be to use the HMI to display a list of alarms, if you're able to access it.
 

Similar Topics

Apologies for not being the best IDEC programmer. I recently was doing some inspections on a site that had 3 FC6A IDEC processors. The issue is...
Replies
0
Views
17
"Hello! Good day! Excuse me, I have a question regarding the 1761-NET-ENI. RSLinx has already detected it but it's not connecting to the PLC...
Replies
4
Views
40
How to fix if appears code “$115 plc-restart running” on the screen OP17
Replies
1
Views
58
Good morning fellow sea captains and wizards, I am being asked to do the above and obtain 4 values from each slave, I know about the MRX and MWX...
Replies
20
Views
153
HI i would like to know how to get a variable that will store the amount of times a program has been executed. The issue is I have 3 DBs for 1 FB...
Replies
2
Views
54
Back
Top Bottom