Producer / Consumer Issue

Dalesey

Member
Join Date
Jun 2012
Location
Middlesbrough
Posts
1
Hi all. Currently got an issue regarding establishing a connection on site between an L55 controller (Consumer) and an L61 controller (Producer). The connection between Ethernet cards is healthy but the controller shows a warning sign.

We currently have producer/consumer tags set up on site between this L55 controller and other L6xx controllers throughout the site that work but this is when the L55 controller is the producer, not consumer. Currently the L6xx series controllers are at version 19.11 and the L55 is at 16.22. Obviously i cannot select the L6xx revision in the L55 PLC so the highest i can select is 16.22.

I've read countless times that "firmware of controllers does not matter" but i have now performed this test in the office with an L63 controller instead of L61 (Don't have an L61 in the office) and when the L63 controller consumes the L55 tag it is fine but doing it the other way round gives me an error code 16#0100 Connection request error. Module in use

L55 Controller version = 16.2
L55 Ethernet version = 4.3

L61 Controller version = 19.11
L61 Ethernet Version = 6.2

Has anyone had an L5xx series PLC consuming a tag created by an L6xx series PLC? a bit stumped!
 
Last edited:
That error can be caused if a controller has reached the maximum number of connections available, or the producer tag is not set-up for the correct number of consumers.

I have certainly seen no issues with tag Produce/Consume between controllers of different firmware revisions.

I have an L62 and a 5550 L1/A and have had no problems producing/consuming either way.
 

Similar Topics

Hi, I am trying to develop a producer/consumer software architecture to use in my automation projects. The idea is to have two tasks, the first...
Replies
2
Views
2,072
I have two ControlLogix PLC talking to each other using producer and consumer model. Is there a way to monitor the health of comm. link?
Replies
10
Views
3,858
Hi I´m testing producer/consumer tags with solftLogix5800 I have try with two configuration: SoftLogix(A) Producer ---------- SoftLogix(B)...
Replies
5
Views
3,196
Guys I do have system (control Logix redundant over ethernet (FOC) to anther/same control logix redundant) i want to use consume and produce...
Replies
14
Views
3,432
im trying to set up some producer/consumer tags to a couple of control logixs im getting this error in 1 of them code 16#0108 connection request...
Replies
5
Views
6,662
Back
Top Bottom