Hi,

I'm trying to reset an unresponsive 1769-L30ER, made more difficult by the fact that I'm separated from it by 100 miles. I have VPN but that's only partly useful.

The LEDs are flashing such that the 1769 may have either a recoverable or unrecoverable error (not very helpful error definition !).

A power cycle has been tried several times - to no avail.

An attempt has been made to find the PLC via BOOTP-DHCP, but discovery doesn't find it.

So, my colleague has connected a client laptop with all Rockwell s/w to the PLC with a USB cable. Windows Device Manager on the laptop shows the attached [WindowsDeviceManager] which looks like the connection isn't quite properly set up, and yet the model of PLC is identifiable ?

Factory Talk Linx Browser shows a network connection node for "USB" but, whilst the three little LEDs on that USB icon blink, no attached device is found.

In RS Linx Classic, I do RS Who, but I don't get the "USB" node appearing in the tree of drivers which the 1769 installation manual promises I will.

Any thoughts if following up on this USB line of attack will prove useful in resetting the PLC, or does it look like a fatal problem ? What should Windows Device Manager be showing, and is there a driver upgrade available ?

Thanks all.
Attached Images
File Type: png WindowsDeviceManager.PNG (6.9 KB, 91 views)
  Reply With Quote
Old May 20th, 2020, 10:28 AM   #2
_Dock_
Member
United States

_Dock_ is offline
 
Join Date: Sep 2015
Location: KY
Posts: 204
You probably need to set up the driver in Linx. If you do not see the usb driver then someone probably deleted it at some point because I believe it is created by default.

Once you have the usb driver in linx you should be able to browse it and see the plc to connect.
  Reply With Quote
Old May 20th, 2020, 10:29 AM   #3
_Dock_
Member
United States

_Dock_ is offline
 
Join Date: Sep 2015
Location: KY
Posts: 204
Post a snip of the rs linx drivers.
  Reply With Quote
Old May 20th, 2020, 10:42 AM   #4
Firejo
Member
United States

Firejo is offline
 
Firejo's Avatar
 
Join Date: Jun 2008
Location: Redmond, WA
Posts: 1,417
Right click on the processor and see if it shows and EDS file to download. It's a bit of a shot in the dark but worth a try.
__________________
Go Hawks!!!
  Reply With Quote
Old May 20th, 2020, 11:16 AM   #5
_Dock_
Member
United States

_Dock_ is offline
 
Join Date: Sep 2015
Location: KY
Posts: 204
Do you have tech connect?

ID: QA14426 | Access Levels: TechConnect
RSLinx Classic USB or VBP Driver: Software Cannot See Controller or Module
  Reply With Quote
Old May 21st, 2020, 10:11 AM   #6
Operaghost
Member
United States

Operaghost is offline
 
Operaghost's Avatar
 
Join Date: Apr 2002
Location: Dallas, TX USA
Posts: 2,787
He cannot right-click on the controller to check for EDS files because he is not seeing the controller. The picture we see is from the Windows Device Manager, not RSLinx.

Also, if you power down a faulted controller and then power it back up it just returns to where it was when it powered down. Cycling power won't clear a fault unless logic has been written to do this.

Try cycling the mode switch to PROGRAM-RUN-PROGRAM to clear the fault. This does not clear the fault code, but does clear the fault.

I believe you might be using an older version of RSLinx that does not have signed Windows CIP/USB drivers. Upgrade to he newest RSLinx and hopefully this will allow you to connect via USB. Once this is done, plugging in to the USB port should automatically create your RSLinx USB driver. It is the only driver that gets added automatically in RSLinx.

OG
  Reply With Quote
Old May 21st, 2020, 04:29 PM   #7
Firejo
Member
United States

Firejo is offline
 
Firejo's Avatar
 
Join Date: Jun 2008
Location: Redmond, WA
Posts: 1,417
I didn't catch that the image posted is from the Device Manager. That changes things. I've seen this before but with a Micro850 and PV800 rather than a CompactLogix. However the problem that I had/have isn't specific to the device, it's a Windows problem. Something corrupted in the drivers association and it no longer gets pointed at RSLinx which is why you see it in "other devices". Unfortunately I've not been able to come up with a fix so I have two Micro850's and one PV800 that I can't connect to RSLinx via USB. I'd call Rockwell (something I have not done) and see if they have a solution.
__________________
Go Hawks!!!
  Reply With Quote
Old May 21st, 2020, 05:10 PM   #8
_Dock_
Member
United States

_Dock_ is offline
 
Join Date: Sep 2015
Location: KY
Posts: 204
FireJo if you can read that tech connect I posted I bet your solution is in there. If not expand on your issue and I’ll translate which solution I think it is in my own writing.
  Reply With Quote
Old May 22nd, 2020, 08:51 AM   #9
rjswagel
Member
United States

rjswagel is offline
 
Join Date: May 2020
Location: Wisconsin
Posts: 20
Try using the AB_VBP-1, 1789-A17/A Virtual Chasis driver.
  Reply With Quote
Old May 22nd, 2020, 08:59 PM   #10
huangshuai
Member
China

huangshuai is offline
 
Join Date: Oct 2019
Location: china
Posts: 8
I have encountered a similar problem before, under the other devices in the device manager, the unknown device is displayed, because the USB driver is not automatically installed, you can find him in the default installation directory of C drive Rockwell, manually install the driver, and then it ’s just
  Reply With Quote
Old May 23rd, 2020, 07:30 PM   #11
Rob S.
Member
United States

Rob S. is offline
 
Join Date: Sep 2008
Location: Maryland
Posts: 696
Could it be the power supply ? I had a SLC 500 5/05 doing something similar a few weeks ago .
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
PID Integral (KI) configuration (RS 5K V. 20.12 1769 L30ER) saultgeorge LIVE PLC Questions And Answers 2 March 12th, 2020 01:40 PM
Migration from micrologix 1500 to compactlogix 1769 l30er akash11132 LIVE PLC Questions And Answers 8 March 25th, 2018 07:56 AM
recommend a usb to ethernet adapter strantor LIVE PLC Questions And Answers 9 September 20th, 2014 11:14 AM
HMI datalogging to USB from CF port (or remote CF port) strantor LIVE PLC Questions And Answers 1 September 5th, 2014 10:20 AM
cable usb proface usb a to usb a onoyjo LIVE PLC Questions And Answers 7 June 25th, 2012 09:41 AM


All times are GMT -4. The time now is 06:44 PM.


.