Logix 5575 - Get Redundant Power Supply Status

Tanquen

Member
Join Date
Jul 2014
Location
CA
Posts
163
I’m using RSLinx to get some of the built in diagnostics items from the PLC. Like @ProcessorName, gets you the name of the program running in processor. Is there nothing for the connected redundant power supplies?
 
There is not.

ControlLogix power supplies do not communicate with the CPU over the backplane, nor does the CPU have the ability to read voltages or discrete signals across the backplane connector.

The Redundant power supplies like the 1756-PA75R have an onboard solid-state output contact for their status, which you would have to wire into a discrete input somewhere in the I/O system.
 
Thanks for the info. That is the way it was looking, I was just thinking that something may be coming through those crazy huge cables from each of the power supplies.
 

Similar Topics

Guys, please help me with this urgently. We have Logic 5575 installed in hot n standby setup. For some reason, the primary now cannot sync with...
Replies
10
Views
377
ControlLogix 5575 (L75): Sudden/Repeating "Unconnected Message Timeout" (0204) This ControlLogix PLC (L75/5575) has been in operation for at...
Replies
24
Views
10,538
Hi Everyone, I am not proficient in RSLogix 500 so I have a question regarding the evaluation of N7:0 data as an input. So as I understand in...
Replies
1
Views
68
Hi folks, in the alarm manager of Rslogix 5000, the tag-based alarm has been created. But when I tried to change the condition, it was found the...
Replies
2
Views
130
I have been working on this for a while now and I can't seem to get it. I was finally able to view the 1500 on the PanelView under the serial...
Replies
1
Views
76
Back
Top Bottom