PowerFlex 755 VFD misrepresenting frequency?

phuz

Member
Join Date
Jun 2008
Location
Mohnton, PA
Posts
1,044
We have a new installation with a brand new PowerFlex 755 (20hp). Motor nameplate is 1175 RPM, yet I was told it was running a little over 1200rpm at 60Hz. Two meters were used to test the output frequency and both verified that the actual output was 2.3Hz higher. What could cause this?
 
We have a new installation with a brand new PowerFlex 755 (20hp). Motor nameplate is 1175 RPM, yet I was told it was running a little over 1200rpm at 60Hz. Two meters were used to test the output frequency and both verified that the actual output was 2.3Hz higher. What could cause this?

Is the VFD putting out 60Hz or 62.3Hz? You're sort of saying it both ways. Also, how do you know the RPM, do you have a tach or encoder? If it's putting out 62.3Hz and you're commanding 60Hz, there may be some sort of slip compensation enabled.

If the drive is putting out 60Hz and the RPM is close to 1200RPM, the motor may just be running at very low load.
 
I would assume that you have slip comp enabled. It is a 1200RPM motor that runs at 1175RPM at 60Hz due to losses. Slip Compensation tells the drive to run at a little higher frequency in order to achieve that perfect 1200RPM.

specifically: Final Freq = 1200/1175 * 60 hz = 62.277 hz
 
Did you check the output frequency or the actual motor speed? If you put a meter on the drive to check the output frequency, it had better be one heck of a sophisticated meter to be able to accurately filter out the hash that is coming from the transistors. The drive (in any kind of vector mode) is looking at the actual motor rotor speed and may be tweaking the output to attain the desired EFFECT in the motor (basically what the others were describing).
 
I just found out some more information.
The output at 60Hz is actually 62.3Hz, but the RPM appears to be "hunting."
It's a very consistent load (several thousand pounds of rotating metal through a few reducing gears) so I wouldn't expect this behavior.
What parameters might affect this?

If you would like it to run at 1175RPM @ 60Hz, enter 1200RPM as the motor nameplate speed.

Why would be enter anything other than the nameplate data?
 
As others have stated, this sound like slip compensation working to keep the motor speed at the requested RPM. In order for anyone to try to give you a better answer more info is needed.

Such as,
1. are you using an encoder,
2. what control mode is the VFD programmed for,
3. have you done all of the auto tuning steps specified in the manual

There are plenty more that I haven't listed but these are a good start.
 
If you would like it to run at 1175RPM @ 60Hz, enter 1200RPM as the motor nameplate speed.

As others have stated, this sound like slip compensation working to keep the motor speed at the requested RPM. In order for anyone to try to give you a better answer more info is needed.

Such as,
1. are you using an encoder,
2. what control mode is the VFD programmed for,
3. have you done all of the auto tuning steps specified in the manual

There are plenty more that I haven't listed but these are a good start.

No encoder, we are just setting a speed and "hoping" the motor follows it.
Pretty sure the VFD is in sensorless vector mode, but I'll confirm when I'm back on site in a few hours.
This is where you slap my wrist because I have NOT done the Autotune. I'll add that to my list for this visit.
 
Last edited:
I managed to find the slip compensation in the drive was set to 249 RPM...wow!
I backed it down to 20 and motor is right on the money.

I tried to do a static tune, rotate tune, and inertia tune, but the drive never moved...it just stuck in a state of waiting.
 
Network-controlled, and while I disabled the "Stop" output (to take the drive out of StopAsserted state), I did not inhibit the drive. I bet that'll do it. I'll try Friday AM.
 

Similar Topics

I have a 1756-L83E PLC and I have a PowerFlex 755 VFD and in the properties in the project I added it to I see in the Date/Time area under clock...
Replies
4
Views
1,630
Hi all, I need help with the parameters to set in order to read motor amperage from this VFD analog output. Thank you!
Replies
11
Views
6,801
So I have a sort of unique situation where I'm wanting to run a PF755 from the IO and over ethernet. Of course, this comes with it's own set of...
Replies
9
Views
254
Hi I was wondering I need to update the firmware of a 755 inverter does the drive hold the program on the drive and just updates the firmware or...
Replies
5
Views
164
So I'm replacing a terminal block on the inverter board for a 755. I'm wondering if anyone knows what conformal coating would be best? I'm not...
Replies
1
Views
132
Back
Top Bottom