rmb550 Member R Join Date Nov 2009 Location Ontario Posts 86 Dec 31, 2011 #1 I have downloaded SimplyModbus and have succeeded in writing values to the PLC, but I cannot seem to read any of the registers. Has anyone had any experience with this? Happy New Year rmb
I have downloaded SimplyModbus and have succeeded in writing values to the PLC, but I cannot seem to read any of the registers. Has anyone had any experience with this? Happy New Year rmb
rmb550 Member OP R Join Date Nov 2009 Location Ontario Posts 86 Dec 31, 2011 #2 OK -- I changed the Slave ID to 1 and voila! there's all my data.
rmb550 Member OP R Join Date Nov 2009 Location Ontario Posts 86 Dec 31, 2011 #3 Ahhhh but a mystery -- it returned the WRONG data. I am stumped.
diat150 Lifetime Supporting Member D Join Date Mar 2006 Location Louisiana Posts 1,474 Dec 31, 2011 #4 it may be offset by 1
Ken Moore Lifetime Supporting Member Join Date May 2004 Location North, West, South Carolina Posts 3,470 Jan 1, 2012 #5 Yes, some vendors start at 0 and some start at 1.