I have an AB system with a Control Logix5000 series processor and a PanelView Plus 700 HMI. They are interconnected through Ethernet.

My problem is after I create a .MER file from the RSView Studio software on my PC and try to download via ethernet I get "Transfer failed due to CIP general status 0x01 extended status 0x0204". I do not know what this is trying to tell me. I have disabled all other When I look at the applications that are loaded on the PV I can see the file I just downloaded but it will not run. Any suggestions?
 
I think I've seen this before.... it's a timeout that happens right at the end of the download process, isn't it ?

The error code is an a generic CIP error code, where 0x01 is a connection manager error and 0x0204 is a timeout.

Check any firewall or VPN software you might be using, including the Windows XP SP2 firewall and CheckPoint SecureRemote. I've seen both of those interfere with RSLinx Enterprise.

I load most of my PanelView terminals via CompactFlash cards. That's the quickest way to get up and running while you troubleshoot this issue.
 
Anyone ever solve this issue? Im getting it as well on a PV+ 400. The PV shows up in the rslinx enterprise browser, and I can ping the PV. Im using the transfer untility. Any Suggestions?

matt

Nevermind, IP Conflict. I guess thats a general timeout error. Thanks anyways
 
Last edited:
I just experienced the same problem with the exxact same fault numbers: Here's what I did to resolve this problem: Are you ready............

Cycled power to the Panel View Plus - that took care of it.đź“š
 

Similar Topics

Am asking if we can upgrade sd ram and cf card of panel view plus ab by a normal sd ram and cf card but Allen Bradley to save cost because in ab...
Replies
9
Views
281
Good morning, I have a question, I would like to know if I can send an Excel file to an email from my panel view and see how it is possible to...
Replies
1
Views
154
I want to run a factory talk view ME project in a Panel View Plus 7 Performance HMI. The project was developed in a 'Windows 7 Professional 64 bit...
Replies
5
Views
332
I purchased a used PanelView Plus 1000 to learn get familiar with the software. Seems to be a pretty popular HMI. I can ping the HMI but I cannot...
Replies
6
Views
884
Hello, hope yall are doing well. I have a HMI program where I need to add a "GoToDisplay" button, so when this button is pressed, it goes to a...
Replies
5
Views
881
Back
Top Bottom