PV Standard Screen Control

I have a SLC 5/04 and PV1000 Standard

In the PV, these tags are defined:

Screen Status Tag = N7:44
Screen Control Tag = N7:43

In the PLC, when one particular alarm occurs, a value of 34 is moved to N7:43, via a one shot. This displays screen 34 as expected.

There is then a rung with the condition that when N7:44 = N7:43, CLR N7:43. The idea is obviously to return screen control to the HMI once the desired screen is displayed. This seems like it should work, but what is observed intermittently is:

Alarm occurs, PV displays screen 34, but PLC retains screen control and operator calls maintenance. I go online and see that N7:43 = 34 and N7:44 = 0.

Does anyone have any idea how / why the status tag can have a value of 0 when the screen being displayed is screen # 34?

Thanks for any help,

Rob
  Reply With Quote
Old October 3rd, 2012, 12:23 PM   #2
Mickey
Lifetime Supporting Member
United States

Mickey is offline
 
Mickey's Avatar
 
Join Date: May 2003
Location: Palmdale,Ca
Posts: 10,149
Maybe the PLC program is also clearing N7:44, take a close look at it's program.

Or post it here and maybe someone can spot something. Zip the program (.RSP file) first then post.
__________________
Mickey

If you want happiness for an hour-take a nap. If you want happiness for a day-go fishing. If you want happiness for a month-getmarried. If you want happiness for a year-inherit a fortune. If you want happiness for a lifetime-help someone else.
----- Chinese Proverb
  Reply With Quote
Old October 3rd, 2012, 12:33 PM   #3
naegely
Member
United States

naegely is offline
 
Join Date: May 2008
Location: Florida
Posts: 90
Thanks for the reply Mickey. That is a good point, I should have mentioned that the only occurence of N7:44 in the program is in the EQU comparison with N7:43.

I wish I could post the program, but unfortunately I'm not permitted to by company policy.

I also should have mentioned that the identical set up and program is running on ~40 machines, and the issue has only been seen on one, and only in the last several days. I've verified no changes have been made to the program. Really strange one, thanks for responding.

Rob
  Reply With Quote
Old October 3rd, 2012, 01:16 PM   #4
Paul351W
Member
United States

Paul351W is offline
 
Join Date: Mar 2008
Location: Northern Illinois
Posts: 145
I have noticed in the past that if there are multiple rungs making changes to the screen control address, it can randomly flicker. I try to set up my screen control such that only one rung that modifies the screen address can be true at one time and that usually fixes the problem.

However, in our setups the PLC always has control of the screen, not the panelview.
  Reply With Quote
Old October 3rd, 2012, 02:25 PM   #5
naegely
Member
United States

naegely is offline
 
Join Date: May 2008
Location: Florida
Posts: 90
Thanks Paul,

We actually have just the one rung changing the screen control tag value
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
a.b pv 600 touch screen arsastry2000 LIVE PLC Questions And Answers 5 May 26th, 2011 04:30 AM
Can't drag faceplate to screen (WinCC Flexible 2007 Standard) Kaspergl LIVE PLC Questions And Answers 0 July 23rd, 2010 08:12 AM
What is D in PID? ... fundamentals of Derivative Ron Beaufort LIVE PLC Questions And Answers 20 March 2nd, 2005 02:26 AM
Panelview Inactivity Screen Control fartinmartin911 LIVE PLC Questions And Answers 2 February 1st, 2005 01:57 PM
PV 600 Color Touch Screen Bob O LIVE PLC Questions And Answers 9 February 25th, 2004 02:11 AM


All times are GMT -5. The time now is 11:36 PM.


.