Output isn't going to 24V on Delta SX2

Sprayman

Member
Join Date
Jan 2020
Location
Chicago
Posts
50
Hi there,

Had a quick question (hopefully).

I am having trouble setting my output to 24v. I am not sure exactly how the inner workings go, but i have a 24v line and a 0v line coming into the output area. When I write Y0 high it should go from its initial 0v to 24v right?

I do not know of anything I would have to do on the code side to setup the output. I am simply just turning on the Y0 coil. i have done a voltage/connection test at every stage of the process. I can't figure out why it wont go high.

any thoughts would be greatly appreciated!!!

Thanks!!!
 
Ok So i figured it out, I assumed the output would give 24v, instead it ties to 0v. My initial relay connection was tied to V- and the output, I switched to connecting to 24v and reversed the connection points. Seems to work fine now. I guess to round off this quesiton, is there a way to output a switching 24v? not sure if thats even possible.

Thanks!

Part number is DVP20SX2
 

Similar Topics

Hey all, I am starting a new project for a customer and I am adding in solenoid valves. Once added, I noticed there was a lack of an Output...
Replies
0
Views
50
Hi, The hardware is: Click Plc model # CO-O1DD1-O HMI model # S3ML-R magnetic-inductive flow meter model # FMM100-1001. I will set the flow meter...
Replies
4
Views
114
Hi, I am using AB 5069-L306ERS2 CPU. My system should achieve SIL-2. I have safety door switches connected to AB 5069-IB8S module, and I want to...
Replies
1
Views
103
Hello! Hope you are great. I need to make a change in a PLC with ladder logic. I will mount a analog valve and I need to control it in ramp up...
Replies
7
Views
292
I have a 170AAO92100 card that I am interested in using as a 10 volt output. Is there setup that I have to do in order to change output or simply...
Replies
0
Views
82
Back
Top Bottom