SLC 5/04, communication instruction

ade

Member
Join Date
Mar 2005
Location
Bandung, West Java, Indonesia
Posts
46
Hello everyone.

Using MSG (Message Read/Write) instruction, can we use this intruction via DH+ communication network within SLC 5/04 processors. I have read the help menu in the RSLogix 500, it doesn't explain this instruction in DH+ network. I want to access some addresses at, let say, SLC#1 and use them in the SLC#2.

Your comments, suggestion and explanation will be greatly appreciated.

Best regards,
ade
 
No the help file doesnt explain well about messaging with DH+.
But the "trick" is that DH+ is Channel 1 in the setup screen for the message instruction.

Thanks Jesper,

Back to the target, how can I access the adresses of the SLC 5/04 processors to be manipulated in the other SLC 5/04 processor which connected via DH+ network. I mean what kind of instruction to be used. The help menu explain it in the DH485 network.

Thanks
 
As Jesper mentioned Channel 1 will give you access to communicate through DH+. Take note the "Control Block" is a set of 14 data words starting the address you assign with. And the data you want to convey is set in the setup screen - "Data table address"

I just noticed your last post after I posted, you do not have to program anything special, the contents in the "Data table address" + the "Size in elements" (words) will be read or write as you assigned in the MSG instruction.
 
Last edited:

Similar Topics

I'll start off by saying I'm unfamiliar with communications between PLC's, hence my question here. We have a machine with a ControlLogix & a SLC...
Replies
7
Views
2,789
Hi, I have a problem with a cpu slc 5/05 (1747-L552), 32k Mem 0S501 series C, I am using the MSG instruction to ethernet communication, it works...
Replies
13
Views
9,281
Hello, I need to connect with a SLC 5/01 (1747-L511) in order to see what is the current program that it has, since I don't have a lot of...
Replies
5
Views
707
After I tried wiring, I used computer program communication to read the PLC N value, but received a NAK signal. And the DL3500 CHA light keeps...
Replies
0
Views
423
Hi all--figured I'd knock the rust off minds here; Situation--We're resurrecting an old Alvey Palletizer from the grave. It came w/o a controller...
Replies
2
Views
943
Back
Top Bottom